Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

How to manage alarms in 9 steps

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • How to manage alarms in 9 steps
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Bastian_Schmitz Champion
38
LeTomas
LeTomas Mentor
14
ismailozinan
ismailozinan Leader
8
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Start a Topic
GMI
GMI
Explorer

Posted: ‎2020-09-03 06:54 AM

1 Like
1
2413
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-03 06:54 AM

How to manage alarms in 9 steps

Originally published on GMI blog by GM International | August 27, 2020

 

How to manage alarms in 9 steps.jpg

 

Alarm systems are essential to manage modern industrial plants. Their operation is fundamental for the production, informing operators and supervisors on possible risks.

 

Alarm management is one of the hottest open discussions in plants automation and maintenance. This is given to some key factors such as risk reduction, people and environment safety, the need to improve alarm systems already present in the plant.  

In the past, it was quite uncommon that the operator had to manage more than one hundred alarms. Usually those alarms were configurable via hardware as with light signals which were expensive and not adaptable. 

With modern automation, alarm system functionalities are achieved through interfaces that are suitable, smaller in dimension, less expensive and that make use of standard and open software components. 

 

Today, the increased number of alarms and warnings, caused by the increased number of connectivity and available data, has a negative impact on working stress. For this reason, companies and associations have faced the problem focusing on analysis and optimization of alarm systems. The most interesting goals reached are the standards AIS/ISA 18.2 and Eemua-191. 

These standards define what an alarm is, emphasizing the response to malfunctions and feedback model. Moreover, they also develop the concept of “Alarm Management Lifecycle” that defines the methodology to classify and realize alarm messages to analyze risks and principles to be adopted in the engineering of control systems. 

 

To be noticed that even international standards, ISA 18.2 and IEC 62682, for alarm system management in process industries, are aligned with Eemua-191. Norms included in EN 50131 should also be taken into consideration, since they describe performances for Intrusion & Hold-Up Alarm Systems (I&HAS) indicating the safety level of the system and of its components. 

 

The 9 steps of Alarm Management 

Alarm Management is necessary in a production environment, controlled by operators using a system for control, maintenance and supervision, with hundreds or thousands of single alarms. At the same time, it is crucial to ensure that all the alarms are shown to operators in a suitable time. Alarms should also be able to provide the operator with the necessary means for intervention basing on priority. To guarantee production continuity, safety and quality 24/7, that is able to react to all the alarms, alerts and anomalies, an organization with a precise strategy must be in place. The following nine steps summarize it.  

 

Step 1: Guide Lines 

It is important realize a document comprehensives of design phase which includes guidelines, defines standards of the plant and the management methodologies of the alarms based on best practice 

  

Step 2: Comparative evaluation 

It is important to analyze the alarm system in order to define its strengths and weaknesses, as well as to find a practical solution to improve performances 

 

Step 3: Documentation and alarm classification 

A revision of documents and of the entire alarm database is useful to guarantee that each alarm conforms to the philosophy and principles of a good alarm management. 

 

Step 4: Alarm system performance definition 

The so called “Alarm System Performance” should be defined with easily accessible metrics, through spreadsheets or structured data bases. Examples of such metrics are the “number of alarms per operator”, alarm frequency, how many hours the alarms were triggered more than a certain amount of times. 

 

Step 5: Control system design 

It is important to design control systems that are capable of configuring several alarms without losing performances and flexibility, as much as to have the possibility of adding and configuring alarms easily and rapidly. 

 

Step 6: KPI 

The alarm system should operate in accordance with KPIs and concepts of ergonomics and Human Factors Engineering. Software tools with specific characteristics and functions are needed to ensure that performances of the entire system are in accordance with the desired final results. 

 

Step 7: Safety design 

When possible, the alarm system must be designed in accordance with IEC 61508 and the required availability specifications. The alarm system should be independent from the control system and from other secondary alarm systems. 

 

Step 8: Defining priorities 

Priorities need to be assigned in order to guarantee that the most critical alarms receive the needed attention by the operator, as soon as possible. Alarms must be presented to the operator in a clear way, depending on their priority and should be distinguished from other alarms, remaining ON and visible as long as the alarm is active. 

 

Step 9: Information for operators 

Alarm configuration must allow operators to take correct evaluations and to take action in a reasonable amount of time. Each alarm should provide the operator enough information on alarm conditions, areas involved, requested actions, priorities, when the alarm was triggered and its status. 

  • Tags:
  • Alarm systems
  • EN 50131
  • english
  • IEC 62682
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
Anonymous user
Not applicable

Posted: ‎2020-09-03 07:39 AM

1 Like
0
2410
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-09-03 07:39 AM

Very valuable and comprehensive article. Thanks for sharing.

 

In this regard I would also like to mention two alerting solutions that can support the alarm management process.

 

SIGNL4 is a lightweight, app-based alerting service for operational teams supporting app push, SMS text, voice calls, escalations, duty planning and collaboration.

https://shop.exchange.se.com/en-US/apps/52175/signl4-instant-mobile-alerting

 

Enterprise Alert is a mature on-premise alerting software.

https://shop.exchange.se.com/en-US/apps/59446/enterprise-alert

 

When critical systems fail or major incidents happen, those alerting solutions help to notify your staff, engineers, or workers ‘in the field’ quickly and no matter where they are.

 

I hope you find this helpful.

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore