Posted: 2023-07-07 08:18 AM
Hi,
I have control expert V15.3 and the hot standby M580 PLC (SV 4.10)
The issue is Control expert (V15.3) showing some error while building the application changes in online mode for HSBY M580 PLC and process failed with error.
Below are the errors for configuration:
- hsby list: Task [MAST] expected number [356], real number [357]
- The Hot standby unlocated data's exchange list contains invalid items. The project must be rebuild all
- Configuration binary generation error.
Does any one know how to resolve this issue. Appreciated your help. Thanks!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-08-23 01:47 AM
Hello AvinashPail,
From the message that you attached, I would say that it is something related to the execution time of the MAST task and the synchronization of the data of the same task. Check that the variable ECPU_HSBY_1.MAST_SYNCHRONIZED is set to one, if you don't need to increase the execution period of the MAST task.
In any case, information would be missing to diagnose the problem. I advise you to contact technical support in your country and share the program in STA, and the PLC diagnostic file.
Good luck!
Ricard
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-20 04:33 AM
Hi I have been experiencing the same.
Was this resolved?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-12-20 04:37 AM
HI, did you get a resolve for this issue at all?
I am experiencing the same.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-01 09:03 AM
Belive this is the same problem I had a year ago. It is a bug that was solved with CE V15.3 Hotfix 6 (that caused another bug that needet hotfix 7). I dont think these files are available, so you need to contact schneider support and ask for a link to download these files.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-03 12:35 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-04 12:25 AM
Maybe HF0012 is the correct one. Seems to have Id numbers pluss more.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-02-04 10:13 PM
Thank you @KJBER for the snaps, will check update here if this HF12 resolving the issue or not.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-30 05:31 AM
hi,
experience the same problem,
I had installed HF12, it cannot fix the problem. Any other suggestion? thank you for your help.
Control Expert Version: V153 - 230214C
Hardware: BMWH584040 (03.20)
Link copied. Please paste this link to share this article on your social media post.