Good day,
We have experienced a communication loss between M580 (via NOC0301.2) and ETG100.
In the PLC program, there is only one READ_VAR function and there is a dedicated section in the program to initialize all timeout to 2000.
When this occured, the timeout was showing 0.
What could be the cause of this ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-04-22 01:51 AM
3 remarks:
1: Your READ_VAR function is using Read_GE1_1_Gest variable. You're setting the timeout in variable Read_GE2_1_Gest, so might be you did not set the timeout at all in (and keeps it as default 0).
2: Timeout of 0 is infinate, makes the READ_VAR wait forever.
3: Timeout value of 2000 corresponds to 2000*100mS = 200 seconds, which is quite long.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-04-22 01:57 AM . Last Modified: 2022-04-22 01:59 AM
Sorry, I made a mistake while copying the section. The timeout is set to 2000 by this code.
Link copied. Please paste this link to share this article on your social media post.