1: Your READ_VAR function is using Read_GE1_1_Gest variable. You're setting the timeout in variable Read_GE2_1_Gest, so might be you did not set the timeout at all in (and keeps it as default 0).
2: Timeout of 0 is infinate, makes the READ_VAR wait forever.
3: Timeout value of 2000 corresponds to 2000*100mS = 200 seconds, which is quite long.