Communication between HMIET6700x and TM262
  • Industrial Automation
  • Communication between HMIET6700x and TM262
Bastian_Schmitz
35
LeTomas
14
JerryBartlemay
7
Posted: ‎2022-06-06 03:44 AM
1
1335
I'm developing a solution the uses the HMIET6700 (vijeo designer basic V1.2) and the plc  TM262 (Machine Expert V2.0.2.1)
the IO manager I'm trying to use is the MachineExpertPacDriveEthernet, when I simulate the HMI application doesn't comunicate with the PLC.
The configurations of the drive are correct (Node name and security settings)
Can I use this drive or do I need to use do Modbus TCP/IP drive? (With this drive I have communication with the HMI and the PLC).
Thanking you for your support.
Bastian_Schmitz
Admiral
Posted: ‎2022-06-07 10:07 PM
TM262 and ESME support since some time user rights managment. The TM262 expect in default configuration credentionals from the HMI through the Codesys (PAC Drive, Somachine) driver. You have to check if this possibility is meanwhile given in Vijeo Designer Basic. In Vijeo Designer this functions was integrated in the last two years.
An other way could be to disable the user rights on the controller. But this would be less safe.
And the last option would be to use the Modbus driver.
  • TM262