New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).
Communication between HMIET6700x and TM262
Industry Automation and Control Forum
This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-0603:44 AM
Communication between HMIET6700x and TM262
I'm developing a solution the uses the HMIET6700 (vijeo designer basic V1.2) and the plc TM262 (Machine Expert V2.0.2.1) the IO manager I'm trying to use is the MachineExpertPacDriveEthernet, when I simulate the HMI application doesn't comunicate with the PLC. The configurations of the drive are correct (Node name and security settings) Can I use this drive or do I need to use do Modbus TCP/IP drive? (With this drive I have communication with the HMI and the PLC).
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-06-0710:07 PM
TM262 and ESME support since some time user rights managment. The TM262 expect in default configuration credentionals from the HMI through the Codesys (PAC Drive, Somachine) driver. You have to check if this possibility is meanwhile given in Vijeo Designer Basic. In Vijeo Designer this functions was integrated in the last two years.
An other way could be to disable the user rights on the controller. But this would be less safe.
And the last option would be to use the Modbus driver.