ATV310 Frequency fluctuation happening

Industry Automation and Control Forum

This forum is addressing industrial automation design & engineering, operations, asset performance, cyber security and digital transformation for Plants & Machines.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • Industry Automation and Control Forum
  • ATV310 Frequency fluctuation happening
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
35
LeTomas
Lt. Commander LeTomas Lt. Commander
14
JerryBartlemay
Lieutenant JG JerryBartlemay Lieutenant JG
7
View All

Recommended Forums

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Related Products
product field
Schneider Electric
Variable Speed Drives and Soft Starters

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industry Automation and Control Forum
Start a Topic
firdaus.alam
Crewman firdaus.alam
Crewman

Posted: ‎2023-03-18 01:37 AM

1 Like
13
8938
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-18 01:37 AM

ATV310 Frequency fluctuation happening

Frequency fluctuation of @ATV310 drive – If I set 25 /30 Hz set point – output frequency is okay from drive and if I set above 30Hz, it give fluctuation in drive output frequency and it varies from setpoint value to maximum frequency. I has also been noted that many times it draws much higher current for same motor and Main voltage (from DC bus) (Modbus Register Address 16#0C87 = 03207) varies a lot. 

 

Please advise Solution for this - it's newly purchased VFD - 2 nos. and both are having this problem

 

Operation is 460Volts, 60 Hz, Location -KSA. 

Attachments
Labels
  • Labels:
  • Asset Performance
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 13
firdaus.alam
Crewman firdaus.alam
Crewman

Posted: ‎2023-03-18 01:55 AM

0 Likes
0
8930
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-18 01:55 AM

The Device Status shows is (Obr)

Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2023-03-19 01:54 PM

0 Likes
6
8916
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-19 01:54 PM

I am not a drive expert, but will offer some things to consider.

 

Start by checking that your ramp settings are sensible.

 

It looks like your drive could be hunting the output frequency to try and control speed.  What motor control mode is it using?  My guess is it is uuC [SVC V].  Try using Std [Standard] V/F, or uF9 [V/F Quad] with an auto-tune.  I have been told by some experts that auto-tune should not be used, and yet in some circumstances this was the only way to make some loads settle down (I have not needed this on a pump before, though).

 

Obr is over-braking, indicating it is ramping down faster than the drive can dissipate heat.  This is probably a symptom of the output hunting rather than inertia or fluid flow causing it to be motored.

Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2023-03-19 06:41 PM

In response to MatthewM
0 Likes
5
8911
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-19 06:41 PM

Opps sorry I was referencing ATV320.  ATV310 has different interface.  Check the Motor Control Type at menu 309.  Auto-tuning is under 318.

Reply

Link copied. Please paste this link to share this article on your social media post.

firdaus.alam
Crewman firdaus.alam
Crewman

Posted: ‎2023-03-20 02:17 AM

In response to MatthewM
0 Likes
4
8888
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-20 02:17 AM

Hi Matthew,

Thanks for your guidance.

 

- 308 - is Maximum Frequency Set which I set 65 Hz whereas 301 (Standard Motor Frequency) I have set for 60 Hz)  - ---- Could this be a Problem?

 

- 318 is Auto Tuning which I have left as Factory Setting "00" which means "NO" ... Do I need to change this? Could this be the reason of this Frequency hunting?

Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2023-03-20 02:29 AM

In response to firdaus.alam
0 Likes
3
8881
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-20 02:29 AM

308 and 301 should be fine.

I would be more interested in what 309 is set to.

Reply

Link copied. Please paste this link to share this article on your social media post.

BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2023-03-20 03:42 AM

0 Likes
2
8876
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-20 03:42 AM

A general comment on drive comissionning, we always advise to enter the motor name plate (with all information such as power, speed, current, ...) and after doing this, perform a motor autotune. This will allow the drive to "know" perfectly the motor. On you case, the OBr is due to motor unstability as it "brakes" when the frequency goes down. You could alos check that speed reference is stable (just to see if it is  a "drive issue", or if this is a "reference issue"). 

Bruno Jacqz, Drives training leader
Reply

Link copied. Please paste this link to share this article on your social media post.

firdaus.alam
Crewman firdaus.alam
Crewman

Posted: ‎2023-03-21 04:08 AM

In response to BJacqz
0 Likes
1
8857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-21 04:08 AM

Thanks for your response, please provide the commissioning document link and in detail procedure for Auto Tuning please if possible.

Reply

Link copied. Please paste this link to share this article on your social media post.

firdaus.alam
Crewman firdaus.alam
Crewman

Posted: ‎2023-03-21 04:09 AM

In response to MatthewM
0 Likes
2
8856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-21 04:09 AM

Hi Mathew,

309 is set to 03 (Standard: 2 point V/F control without internal speed loop).

Reply

Link copied. Please paste this link to share this article on your social media post.

BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2023-03-21 06:46 AM

In response to firdaus.alam
1 Like
0
8849
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-21 06:46 AM

Here you are the user's manual on ATV310.

Bruno Jacqz, Drives training leader
Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

MatthewM
Lt. Commander MatthewM
Lt. Commander

Posted: ‎2023-03-21 02:18 PM

In response to firdaus.alam
0 Likes
1
8844
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-21 02:18 PM

Hmm.  Not behaviour I would expect for 2pt V/F.

As per BJacqz reply, check all nameplate settings are correct, and then perform an auto-tune.  The procedure is described in the manual under 318 "Auto-tuning".

Check that the ramp settings are sensible.  I would suggest it should be 5s or more.

Reply

Link copied. Please paste this link to share this article on your social media post.

firdaus.alam
Crewman firdaus.alam
Crewman

Posted: ‎2023-03-28 04:08 AM

In response to MatthewM
0 Likes
0
8793
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-28 04:08 AM

Motor name plate details input correctly, Auto Tuning done and then started the Motor - Pump.

 

It's doing lot of noise - the pump draws 11 Amps with DOL panel and this VFD causing same pump to draw 18-22 Amps and lot of noise.  

 

Please refer the attached video, please read pump KW in HMI with 1 place decimal (160KW = 16.0KW)

Attachments
Reply

Link copied. Please paste this link to share this article on your social media post.

firdaus.alam
Crewman firdaus.alam
Crewman

Posted: ‎2023-03-28 04:14 AM

0 Likes
1
8791
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-28 04:14 AM

https://www.youtube.com/watch?v=tcRUbYMauPY  - Auto Tuning

https://www.youtube.com/watch?v=koTVM9bR29I  - Motor Parameter Setting

https://www.youtube.com/shorts/tfPwOWFrYiI - Drive Status 

 

Please review these and advise what's causing motor to make lot of noise and draw high Amps (17-22 Amps) whereas same motor on DOL starter is drawing 10-11 Amps.

Reply

Link copied. Please paste this link to share this article on your social media post.

BJacqz
Commander BJacqz Commander
Commander

Posted: ‎2023-03-28 06:36 AM

In response to firdaus.alam
0 Likes
0
8778
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-28 06:36 AM

Hello,

Based on our remarks we can see that motor parameters entered and Autotune done is not satisfactory. 

According to your movie, I see 307 = 3400, is it the nominal motor speed ? I have seen 302 = 7.5 is it the correct motor power ? Then 314 ? 

The next topic to check is the vector control values (setting 320), you can try to change in order to underflux  the motor (decreasing the voltage value of the curve, see on p 57 of manual I gave you). Did you check the motor speed at lower frequencies just to see if the motor is running correctly at lower speed?

On a general poitn of view, I would sayt that if motor current is much higher than normal, it means the ration voltage frequency is not good, this is the way I suggest you to investigate. 

Hope it helps 

Bruno Jacqz, Drives training leader
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore