EcoStruxure Automation Expert and AVEVA System Platform, Galaxy backup migration

Industrial Automation Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Industrial Automation experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Industrial Automation Knowledge Base
  • EcoStruxure Automation Expert and AVEVA System Platform, Galaxy backup migration
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertSanders
    RobertSanders
  • Vartika
    Vartika
Related Products
product field
AVEVA Group PLC
AVEVA System Platform

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industrial Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
582 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EcoStruxure Automation Expert and AVEVA System Platform, Galaxy backup migration

Lt. Commander RobertSanders Lt. Commander
‎2023-06-01 06:47 AM

Last Updated: Lieutenant Vartika ‎2023-11-21 02:07 AM

Caution.png

Issue

When using EcoStruxure Automation Expert V22.1 and AVEVA System Platform the Galaxy project needs to contain all the templates associated with EcoStruxure Automation Expert AppCommonProcess Library, by default the Galaxy backup supplied by EcoStruxure Automation Expert V22.1 is for AVEVA System Platform 2020 R2 SP1. To use a newer version of AVEVA System Platform requires migration.

Resolution

The following knowledge base article details how to migrate the Galaxy backup supplied by EcoStruxure Automation Expert V22.1 to AVEVA System Platform 2023.

The first time EcoStruxure Automation Expert is used to create a AVEVA System Platform Galaxy, it will copy the Galaxy project supplied as part of the installation (called CFLBlankGalaxy) from the ASP Library folder to the AVEVA System Platform BackupGalaxies folder.

RobertSanders_0-1685627080905.png

 

Once the Galaxy backup has been copied, it will then create all other projects based upon this backup. The aim is to replace this backup file with a fully migrated version.

 

 

Step 1 – Create a temporary EcoStruxure Automation Expert Solution

Create a temporary solution and right click on the solution and select Configuration>AVEVA SP Configuration 

RobertSanders_1-1685627080909.png

 

 

Give the new Galaxy project any name and click Create

RobertSanders_2-1685627080911.png

 

After some time you will notice a message in the Output window saying ‘Galaxy needs to be migrated manually’.

RobertSanders_3-1685627080912.png

 

Cancel the System Platform Configuration form.

 

Step 2 – Migrate the Galaxy project 

Open System Platform IDE and select On Server and double click on the project created by EcoStruxure Automation Expert.

RobertSanders_4-1685627080915.png

 

A message will be displayed asking if you want to migrate, select Yes

RobertSanders_5-1685627080916.png

 

The migration will start and will take some time (around 45 minutes), once the migration is complete click the Close button.

RobertSanders_6-1685627080917.png

 

Once the Close button has been clicked you will be asked to log in. The default username and password is Administrator and password left blank.

RobertSanders_7-1685627080918.png

 

When the AVEVA System Platform IDE opens, close without making any changes.

 

Step 3 – Create a Galaxy Backup from the Migrate project 

Open the Operations Control Management Console

RobertSanders_8-1685627080920.png

 

Navigate to the newly created Galaxy project and right click and select Backup.

RobertSanders_9-1685627080922.png

 

Confirm that you want to create a Backup by clicking Yes

RobertSanders_10-1685627080922.png

 

Save the backup to a known folder, e.g., Downloads and name it CFLBlankGalaxy

RobertSanders_11-1685627080924.png

 

 

Step 4 – Copy the new CFLBlankGalaxy over the old

Copy and Replace the newly-created Backup to the BackupGalaxies Folder

RobertSanders_12-1685627080926.png

 

 

From this point on Automation Expert will create any new Galaxy projects using the migrated CFLBlankGalaxy backup.

.

Disclaimer

The views and opinions expressed in this article are those of the author(s) and do not necessarily reflect the official policy or position of Schneider Electric.

 

Labels (2)
Labels:
  • AVEVA System Platform
  • EcoStruxure Automation Expert
Was this article helpful? Yes No
Rate this article:
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore