EcoStruxure Automation Expert – Creating a Faceplate within AVEVA Industrial Graphics

Industrial Automation Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Industrial Automation experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Industrial Automation Knowledge Base
  • EcoStruxure Automation Expert – Creating a Faceplate within AVEVA Industrial Graphics
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertSanders
    RobertSanders
Related Products
product field
AVEVA Group PLC
AVEVA System Platform

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Industrial Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
804 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

EcoStruxure Automation Expert – Creating a Faceplate within AVEVA Industrial Graphics

Lt. Commander RobertSanders Lt. Commander
‎2024-01-10 06:00 AM

on ‎2024-01-10 06:00 AM

Caution.png

Issue

 

Most Common Process Library objects (e.g., Valve) include a Faceplate for control and setup.  

RobertSanders_3-1704894451313.png

 

The Common Process Library uses the supplied Schneider Electric OMI Layout in AVEVA System Platform.

RobertSanders_4-1704894467896.png

 

Resolution

 

The following Knowledge Base article details the steps required to create a Faceplate and associate it with a CAT, using AVEVA Industrial Graphics in EcoStruxure Automation Expert and the Schneider Electric supplied OMI Layout.

The example below is based upon a Valve CAT called MyValve and has the following:

 

Function Block Network

RobertSanders_5-1704894488739.png

 

HMI Interface (iThis)

One input for a Valve open feedback and one output for the Valve open command.

RobertSanders_6-1704894488743.png

 

AVEVA Industrial Graphics – Valve Symbol

The two-way Valve symbol has been assigned to the OpenFB (open feedback).

RobertSanders_7-1704894488749.png

 

 

Step 1 – Make the symbol at runtime selectable.

1, Select the Valve Symbol within the CAT.

2. Select the Property TreatAsIcon and set to True.

 

RobertSanders_8-1704894542133.png

 

 

Step 2 – Add the script to display the Faceplate content.

  1. With the Symbol selected, right-click edit animation.

 

RobertSanders_9-1704894542138.png

 

 

  1. Click the Add button at the top and select Action Scripts.

 

RobertSanders_10-1704894542140.png

 

  1. Paste the following code into the script and click OK.

 

dim contentInfo as aaContent.ContentInfo;

 

contentInfo.Content = FaceplateSymbol;

 

ShowContent ( contentInfo );

 

RobertSanders_11-1704894542142.png

 

  1. The above script uses a Custom Property called FaceplateSymbol - create the property by selecting whitespace (de-select the Valve symbol) then right-click Custom Properties.

 

RobertSanders_12-1704894542143.png

 

  1. Click the Add button and give the name FaceplateSymbol and set data type to String.
  2. The Default value requires setting to the CAT name and Faceplate name.  In this example the CAT name is MyValve and the Faceplate is going to be called Faceplate (e.g, Me.MyValve_Faceplate).

 

RobertSanders_13-1704894542146.png

 

  1. Save and Close the Symbol.

Step 3 – Add the Faceplate

  1. Add a new AVEVA Industrial Graphics and call it Faceplate.

 

RobertSanders_14-1704894542147.png

 

 

  1. In the Properties change the Content Type to Faceplate.

 

RobertSanders_15-1704894542152.png

 

 

  1. Add the required Actions to the Faceplate e.g., Button.

 

RobertSanders_16-1704894542158.png

 

 

  1. Save and Close.

Step 4 – Testing  

  1. Create / Update the new template in AVEVA System Platform by using Sync AutoMapped .
RobertSanders_17-1704894542160.png

 

  1. Once the Template has been created in AVEVA System Platform, use the CAT in your applications and synchronize to System Platform via the normal method, using the Deploy and Diagnostic Tab.

 

RobertSanders_18-1704894542161.png

 

 

  1. Deploy and test – clicking on the Valve will make the Faceplate appear to the right.

 

RobertSanders_19-1704894542163.png

 

Disclaimer

The views and opinions expressed in this article are those of the author(s) and do not necessarily reflect the official policy or position of Schneider Electric.

 

Labels (1)
Labels:
  • dPAC
Was this article helpful? Yes No
Rate this article:
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore