Configuring disaster recovery

ITA installation and setup

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT Help Center
  • EcoStruxure IT Help Center Categories
  • IT Advisor
  • ITA installation and setup
  • ITA installation and setup
  • Configuring disaster recovery
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • EcoStruxure IT Forum

  • APC UPS Data Center & Enterprise Solutions Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

EcoStruxure IT Support

Submit a support request for additional assistance with EcoStruxure IT software.

Request Support
Back to ITA installation and setup
Start a Topic
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
1522 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Configuring disaster recovery

Picard EcoStruxureIT
‎2019-10-14 08:34 AM

Last Updated: Sisko JLehr Sisko ‎2024-04-05 11:07 AM

Note: Licensing for one disaster recovery node (DR) is part of the IT Advisor base license.

In this example of configuring IT Advisor disaster recovery, two stand alone servers have been created, Server1 and Server2. Server2 will be configured as the disaster recovery node to Server1.

 

IMPORTANT: If the Disaster Recovery node is monitored by Data Center Expert via SNMP, it is important to set the device scan timeout in DCE high enough for the Disaster Recovery node to respond. Otherwise, it will return a communication lost status. How you set the device scan timeout depends on the network speed between the Disaster Recovery node and the ITA server.

 

Configure Server 1

 

  1. Log in to the Server1 Webmin interface, and select EcoStruxure IT Advisor > Disaster Recovery.

  2. Select Allow another node to connect to this node.

  3. In Allow the following IP as disaster recovery node, enter the IP address for Server2.

  4. Click Attach. img_01_360036883074.JPGimg_01_360036883074.JPG

  5. Check Accept fingerprint then click Allow.

    img_02_360036883074.JPGimg_02_360036883074.JPG

Once the fingerprint is added successfully, follow the on-screen instruction to go to Webmin for Server2 to continue the setup.  

ITA_dis_rec_82020_360036883074.JPGITA_dis_rec_82020_360036883074.JPG

 

Configure Server 2

 

    1. Log in to the Server 2 Webmin interface and select EcoStruxure IT Advisor > Disaster Recovery.

    2. Select Attach this node (xx.xx.xx.xx) as a disaster recovery node to another node. ITA_1_360036883074.pngITA_1_360036883074.png
    3. Enter the IP address for Server1 in Attach this node to the following IP: ITA_2_360036883074.pngITA_2_360036883074.png
    4. Click Attach. ITA_3_360036883074.pngITA_3_360036883074.png  img_04_360036883074.JPGimg_04_360036883074.JPG
    5. Check Accept fingerprint. ITA_1_360036883074.pngITA_1_360036883074.png and then click Attach.ITA_2_360036883074.pngITA_2_360036883074.png    

      img_05_360036883074.JPGimg_05_360036883074.JPG

 

 

While the node is successfully being attaching, the notification is Attaching the node, please wait this could take several minutes......

 

Please watch the status page to monitor progress.

 

img_06_360036883074.JPGimg_06_360036883074.JPG

 

The Server1 Status page displays information for both itself and Server2 as Disaster Recovery.

 

img_07_360036883074.JPGimg_07_360036883074.JPG

 

The Server2 Status page displays information only about itself as Disaster Recovery.

 

img_08_360036883074.JPGimg_08_360036883074.JPG

 

Upgrading a disaster recovery setup

 

Upgrade both the master node and the disaster recovery node to the new version of IT Advisor.

Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore