Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Logic Configurable ModbusTCP in EcoStruxure Machine Expert HVAC

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Logic Configurable ModbusTCP in EcoStruxure Machine Expert HVAC
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
FedericoM Mentor
119
Bastian_Schmitz
Bastian_Schmitz Champion
64
M_Cervati
M_Cervati Troubleshooter
18
View All

Recommended Forums

  • Industry Automation and Control Forum

  • Machine and Motion Control Forum

  • Alliance Partner Program System Integrator

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to HVAC and Pumping Forum
Start a Topic
Solved
DVarnerMinn
DVarnerMinn
Contributor

Posted: ‎2022-04-28 08:33 AM

1 Like
10
5980
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-28 08:33 AM

Logic Configurable ModbusTCP in EcoStruxure Machine Expert HVAC

Hello,

 

Does anyone know if there is a way within logic for an OEM application being written to be able to change the IP address of a ModbusTCP device?

 

I would like to be able to modify this from a embedded web page.

 

So far, I have not found a way to modify the CONNEC.PAR file that is downloaded (not recommended or desired) or found something like the ModbusMasterRTU functions for ModbusTCP.

 

Thanks

Labels
  • Labels:
  • HVAC
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Bastian_Schmitz
Bastian_Schmitz Champion
Champion

Posted: ‎2022-05-01 10:53 PM

In response to DVarnerMinn
2 Likes
3
5872
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-01 10:53 PM

You could find here a documentation which describe the functions.

Link 

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-05-02 12:15 AM

In response to DVarnerMinn
2 Likes
1
5862
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-02 12:15 AM

@DVarnerMinn,

 

I have attached an example and a short draft document which explains how to create a project with Dynamic Ip settings of the Modbus TCP.

In the project you'll find also how the file is created using the FS_IEC library.

 

BR,

Federico

See Answer In Context

Attachments
TestDynamicConnIP.zip
  • Tags:
  • english
  • M172
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 10
FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-04-28 08:40 AM

1 Like
9
5974
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-28 08:40 AM

Hello,

 

target blocks which allow to send Modbus/TCP messages from background task will be added in the coming release of Ecostruxure Machine Expert HVAC 1.5.0 planned in July/August.

 

With the current version the only workaround is create runtime the CONNEC.PAR using the FS_IEC library and reboot the controller.

Actually M172 loads any file .PAR as a CONNEC.PAR, you could also remove the modbus/TCP part from the CONNEC.PAR and move it on a new file MTCPCLI.PAR which can be updated runtime by the M172

 

Federico

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

DVarnerMinn
DVarnerMinn
Contributor

Posted: ‎2022-04-28 08:55 AM

In response to FedericoM
0 Likes
1
5971
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-28 08:55 AM

@FedericoM 

 

Do you know if Machine Expert HVAC 1.5.0 would also allow the same thing for CANOpen?

 

It might be helpful for us to add or remove expansion I/O using one configurable program.

 

 

Thanks

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-04-28 12:26 PM . Last Modified: ‎2022-04-28 12:27 PM

In response to DVarnerMinn
0 Likes
0
5951
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-28 12:26 PM . Last Modified: ‎2022-04-28 12:27 PM

In the next version 1.5.0, it will be added a target block which allow to read SDO (at the moment is available only write).

 

In the current version, you can define the maximum number of expansions your project might need.

If an expansion is not present is not causing any runtime delay. Just at boot you will have 10sec delay for each missing expansion.

Also this delay can be avoided by setting parameter CANExpPresenceByPar and rebooting the M172.

 

Regards,

Federico

 

  • Tags:
  • english
  • M172
Reply

Link copied. Please paste this link to share this article on your social media post.

DVarnerMinn
DVarnerMinn
Contributor

Posted: ‎2022-04-29 02:00 PM

In response to FedericoM
0 Likes
6
5929
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-04-29 02:00 PM

@FedericoM 

 

Do you know if there is a document on the FS_IEC library available?

 

I can figure out how to use the library but I like to know how and where to find the information.

 

Thanks

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Bastian_Schmitz
Bastian_Schmitz Champion
Champion

Posted: ‎2022-05-01 10:53 PM

In response to DVarnerMinn
2 Likes
3
5873
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-01 10:53 PM

You could find here a documentation which describe the functions.

Link 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-05-02 12:15 AM

In response to DVarnerMinn
2 Likes
1
5863
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-02 12:15 AM

@DVarnerMinn,

 

I have attached an example and a short draft document which explains how to create a project with Dynamic Ip settings of the Modbus TCP.

In the project you'll find also how the file is created using the FS_IEC library.

 

BR,

Federico

Attachments
TestDynamicConnIP.zip
  • Tags:
  • english
  • M172
Reply

Link copied. Please paste this link to share this article on your social media post.

DVarnerMinn
DVarnerMinn
Contributor

Posted: ‎2022-05-02 07:21 AM

In response to Bastian_Schmitz
0 Likes
2
5840
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-02 07:21 AM

Thanks, a few questions.

 

 

What is the difference between Free Evolution and Free Advance controllers?

 

I believe that M172P are the Free Advance models from the looks.

 

 

Where did you find this application note? I haven't looked at the Eliwell website enough to find application notes yet. (I am registered with the website.)

 

 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

DVarnerMinn
DVarnerMinn
Contributor

Posted: ‎2022-05-02 07:24 AM

In response to FedericoM
0 Likes
0
5838
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-02 07:24 AM

@FedericoM 

 

Thanks, I will take a look at this.

 

I have found in the past that I can learn much from example logic from others no matter what the skill set I or others have.

 

 

  • Tags:
  • english
  • hvac
  • M172P
Reply

Link copied. Please paste this link to share this article on your social media post.

FedericoM
FedericoM Mentor
Mentor

Posted: ‎2022-05-02 07:36 AM

In response to DVarnerMinn
0 Likes
1
5835
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-02 07:36 AM

Free Evolution is the Eliwell branded version of M171P, while Free Advance controller is the equivalent of M172P.

 

Actually this application note is quite old, it is available to customers with access to the restricted area of the Eliwell website.

It does not include the latest features included in Ecostruxure Machine Expert HVAC.

 

In terms of FS_IEC description, I think the contents are the same you have when you look at each block description inside the library.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

DVarnerMinn
DVarnerMinn
Contributor

Posted: ‎2022-05-02 07:41 AM

In response to FedericoM
0 Likes
0
5832
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-05-02 07:41 AM

Getting to the restricted area is what I'm not easily finding.

 

I believe I might have some access to it but the link is on my work laptop and I don't go in until tomorrow.

 

  • Tags:
  • eliwell
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore