Communication between M171ODM14R and M172PDG42R with modbus

HVAC and Pumping Forum

Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Industrial Automation
  • HVAC and Pumping Forum
  • Communication between M171ODM14R and M172PDG42R with modbus
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
FedericoM
Commander FedericoM Commander
77
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
52
LeTomas
Lt. Commander LeTomas Lt. Commander
14
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to HVAC and Pumping Forum
dmuzina
Lieutenant JG dmuzina
Lieutenant JG

Posted: ‎2024-05-14 02:14 AM

0 Likes
7
1015
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-14 02:14 AM

Communication between M171ODM14R and M172PDG42R with modbus

Hello,

 

I need to exchange data between this two devices via modbus. Can someone explain it to me how to do it properly?

Labels
  • Labels:
  • Connectivity
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2024-05-15 06:50 AM

0 Likes
1
979
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-15 06:50 AM

Hi You could acitivate on TM172 in ESME HVAC in the configuration tab the Modbus Master functionality on RS485-2. After that you could add a generic Modbus Object and FC3 to read data from the TM171ODM14R. You could see the process in this video. The related Modbus Register for the IOs of TM171O are declared in the User Manual.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
dmuzina
Lieutenant JG dmuzina
Lieutenant JG

Posted: ‎2024-05-16 11:49 PM

In response to Bastian_Schmitz
0 Likes
0
956
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-16 11:49 PM

@Bastian_Schmitz  My 171O says that have only master configuration. I need it as a slave not master is that posibble?

dmuzina_0-1715928524197.png

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2024-05-20 10:55 PM

0 Likes
1
906
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-20 10:55 PM

The standard firmware of TM171O offers the possibility to use a Modbus Master. But this function get only into account if you add messages to the Master tab and activated their the Master ability. 

Bastian_Schmitz_0-1716270834054.png

If the master is not active you act as Modbus Slave. 

In that case are the Register addresses from Status, BIOS and EEPROM are read and write able via modbus.

Status variables could be configured as Readonly.

Bastian_Schmitz_1-1716270931993.png

 

 

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
dmuzina
Lieutenant JG dmuzina
Lieutenant JG

Posted: ‎2024-05-20 11:14 PM

In response to Bastian_Schmitz
0 Likes
0
904
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-20 11:14 PM

@Bastian_Schmitz I put another firmware 412.21 so that it can be slave only, because I didnt know about this information you mentioned above but still I can not get connection. I will put picture here how I made configuration so you can check and tell me if I made something wrong.

Slave M171 configuration:

dmuzina_0-1716271817366.png

Master configuration M172:

dmuzina_1-1716271851346.pngdmuzina_2-1716271869253.pngdmuzina_3-1716271891141.png

dmuzina_4-1716272060842.png

 

In M171 on address 9280 I have WORD variable configured with value 99 but I dont read anything.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2024-05-20 11:25 PM

0 Likes
1
903
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-20 11:25 PM

Hi, did you use RS485-2 on TM172? Did you check the wiring and try to change +/- ? Please disconnect with TM171ADMIN from TM171ODM14R if you want to connect via TM172.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
dmuzina
Lieutenant JG dmuzina
Lieutenant JG

Posted: ‎2024-05-20 11:47 PM

In response to Bastian_Schmitz
0 Likes
0
884
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-20 11:47 PM

@Bastian_Schmitz Yes I am using RS485-2. Wiring is good because i try this on my desk in office and need implement that on the field. I need connect 4 M171 as slave to M172 Master. So i try to make that connection im my office first. 

Yes I have also read that TTL communication can not work together with RS485 so I dissconnect from TTL and yuse just RS485 but without success.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Bastian_Schmitz
Admiral Bastian_Schmitz Admiral
Admiral

Posted: ‎2024-05-21 12:02 PM

0 Likes
0
865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2024-05-21 12:02 PM

The response 2 is normally an indicator that there is a general communicaiton issue. Otherwise the response in sysMbmrtunodestatus would be higher. Do you use a 120 ohm resistor at on or booth ends of the line. Mostly it work on TM172 also without resistor, but not in any case.

You could also try to test the communication to TM171O via a USB/RS485 and a third party tool like Modbus Poll. This could be help to indentifie if the problem is on the side of TM172 or on TM171O.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of