Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Can't Reset GW2-010-00 to reset IP configuration
HVAC and Pumping Forum
Support Forum for HVAC and pumping machines, Modicon M17x and EcoStruxure Machine Expert HVAC software for chillers, AHU, CRAC units for datacenters or process chillers applications - from design, implementation to troubleshooting and more, by Schneider Electric.
Search in
Improve your search experience:
Exact phrase→Use quotes " "(e.g., "error 404")
Wildcard→Use * for partial words(e.g., build*, *tion)
AND / OR→Combine keywords(e.g., login AND error, login OR sign‑in)
Keep it short→Use 2–3 relevant words, not full sentences
Filters→Narrow results by section(Knowledge Base, Users, Products)
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-1711:00 PM. Last Modified: 2021-10-2009:58 PM
Can't Reset GW2-010-00 to reset IP configuration
Replaced an old, but working telemecanique soft starter with a new AYS22D75Q for a 30kw cement mixer wired in Delta.
When I start the motor it runs for a moment then faults out on SCF... strange this is when I change the DLTA parameter back to LINE the motor seems to run fine under no load.
I'll be going back tomorrow morning to run under load but I'm expecting some high Amps and higher temps. I have very limited experience with Schneider gear so anyone has any suggestions I'd appreciate it!
Tested insulation resistance of the motor and the cable, they both passed.
Tested motor windings resistance, with all 3 windings reading around 1.3ohms