Posted: 2025-03-30 10:48 AM
Hello, I would like to retrieve a BACnet value (PresentValue) from another BACnet controller. How can I create a BACnet reference? e.g.: for [178150][5,2] (Device)(Bin.-Val.,2).
- on a TM172PDG18R
- with Eco Struxure Machine Expert-HVAC V.1.7.0
Thank you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-02 12:13 AM
Hello,
client functionalities are not supported by current version of TM172 bios.
It should be implemented in one of the updates planned in 2025.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-04-02 12:13 AM
Hello,
client functionalities are not supported by current version of TM172 bios.
It should be implemented in one of the updates planned in 2025.