I need to share values from my PLC over BACnet and I have the analog working as I imported the "AI" template, but there is no template for "BI", only "BV". When I try to change from BV to BI the drop down is greyed out. How do i share BACnet Binary Input objects with M172 PLC to a BMS.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-25 11:41 PM
Only Binary Value is actally integrated in TM172.
But there should come an update which allows this in the future.