Sending Crystal Reports to Users via Email

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • Sending Crystal Reports to Users via Email
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 11:49 AM
0 Likes
0
4558
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 11:49 AM

Sending Crystal Reports to Users via Email

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 08:49 PM

📖 Home  Back  
Crystal Reports requires an email client to be configured that can be used to send reports via email. Whereas email alarm redirection is performed in ClearSCADA using standard SMTP protocols, Crystal requires a third party email client to do the work.

Since Windows operating systems include Outlook Express as standard, this article describes the use of Outlook Express as the email client that Crystal can use.

Security settings in 'Microsoft Outlook' stop crystal reports from exporting as an email. This is due to Outlook not allowing third party applications to send mail using the Outlook client without notification. ClearSCADA and Crystal Reports requires that this be a seamless process ie. no dialogs displayed when this takes place.


The steps below describe configuring ClearSCADA and Outlook Express to export via email.

Create a Windows User Account



This is the computer user account that ClearSCADA will use to access the computer. Since ClearSCADA runs under the system account by default, it will need to use this account to be able to interact with the system to send the email.

This user account must have 'Logon as a Service' permission. Open 'Local Security Policy' under the Administrative Tools section of the Control Panel. Under 'Security Settings' expand 'Local Policies' Click on 'User Rights Assignment' and add this user account to Logon as a Service.

Log off Windows and log on as the new user you just created.

Setup and Test the Users Email



Open Outlook Express. If you cannot find Outlook Express in the Start Menu, enter msimn.exe from the Run option.

In Outlook Express:
  • In the Tools menu, select Accounts.

  • Click the 'Add' button and select 'Mail...'

  • Enter in your display name and click 'Next'

  • Enter in the email address you wish to use when sending emails and click 'Next'

  • Setup the details of your mail server and click 'Next'

  • Enter in the account name and password for your email account with the remember password selected. Then click Next.

  • Click Finish.

  • Close the 'Internet accounts' window


Test that this email account can be used to send email. If it will not work here, it will not work when using ClearSCADA.

Setup the default email client settings



There are some settings required in Outlook Express to allow external applications to use this email client.
  • In the Tools menu, select Options

  • Select the Security tab

  • Deselect the 'Warn me when other applications try to send mail as me' field

  • Select the Send tab

  • Deselect the 'Save copy of sent messages in the Sent Items folder' option.

  • Click OK to close the Options dialog.


Configure ClearSCADA Printing User



Now that a user has been configured and the email client has been configured, it is necessary to tell ClearSCADA the details of the user account it requires for sending emails and printing.

Configure the username, password and domain (if applicable) in the Server Configuration tool under System Configuration - Printing.
  • Apply the changes and restart the ClearSCADA server.


Set Outlook Express as the Default Mail Client



So that ClearSCADA can use the email client configured, Outlook Express must be the default mail client.
  • Open 'Add / Remove Programs' in the control panel

  • Select 'Set Program Access and Defaults'

  • Expand the Custom tab

  • For Default Email Program select Outlook Express


Configure ClearSCADA to Export Report to Email



To configure ClearSCADA to redirect the report to email:
  • On the Crystal Report, select the Export Format required. This file format will be used to generate the report and will be attached to the email transmission.

  • On the Export Destination tab, select E-mail.

  • Select a user to address the report to, ensuring that they have an email address configured in the user profile.

  • Configure a Subject and Message if required.


All that is left to do is to Export the report and verify that it was attached to the email and sent as required.

Go: Home Back

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore