Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Network Ports used by Geo SCADA

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • Network Ports used by Geo SCADA
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 02:53 PM
1 Like
0
5126
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 02:53 PM

Network Ports used by Geo SCADA

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 11:53 PM

📖 Home  Back  
This article details ports used by Geo SCADA and should form the basis for configuration of system firewalls. For client-server connections, you need to create the firewall rules as described here.

The following table includes details about the protocols and ports used by the other Geo SCADA components, such as drivers. You may need to create firewall rules for those components and features (if any) that your system is using.

The information is categorized under these headings:

  • Protocol - Indicates the protocol used by the port (TCP or UDP)
  • Port(s) - Shows the port or ports that are used by the server or clients. The table shows the numbers for the default ports (you can configure your system to use different ports)
  • Incoming Connection - Indicates the component that receives the connection request
  • Outgoing Connection - Indicates the component that attempts to open the connection



  Protocol   Port(s)   Incoming Connection   Outgoing Connection   Description
  TCP or UDP   -   Devices   Drivers   The protocol and ports used by TCP/IP channels for the connections between the devices and the drivers.

You can configure the protocol and port by adjusting the Port and TCP/IP Type settings on the Connection tab of the Channel Form in ViewX.
  TCP or UDP   -   Outstations   Drivers   The protocol and ports used by network outstations (outstations that have Ethernet ports that are connected to a network).

You can configure the port by adjusting the Port
setting(s) on the Network tab of the Outstation Form in ViewX. The protocol for the port(s) is defined by the outstation's network channel (see below).
  TCP or UDP   -   Drivers   Outstations   The protocol and ports used by network channels (channels that are used to connect to network outstations - see above).

You can configure the protocol and port by adjusting the Listen Port\Port and TCP/IP Type settings on the Connection tab of the Channel Form in ViewX.
  TCP   502   Outstations   Modbus Driver   The port is used by Modbus TCP outstations.

You can configure the port by adjusting the Port setting on the Primary Port and Secondary Port tabs of the Scanner Form in ViewX.
  TCP   502   Modbus Slave Driver   Modbus TCP Masters   The port is used by Modbus TCP slave outstations.

This port is fixed and cannot be re-configured.
  ICMP     Any Network Device   ICMP Driver   Used to test the connection between the main server and any network device. A ping is used to test the connection.

You can configure the device by adjusting the Device setting on the Digital Point tab of the Point Form in ViewX. The ICMP protocol does not have ports.
  TCP   102   Siemens PLCs   Simatic S7 Driver   The port is used by Siemens Simatic S7 network scanners.

You can configure the port by adjusting the Port settings on the Primary Connection and Secondary Connection tabs on the Scanner Form in ViewX.
  TCP   -   OPC XML-DA Servers   OPC XML-DA Driver   The port is used by OPC XML-DA servers.

You can configure the port by adjusting the OPC Server URL setting on the Server tab of the Server Form in ViewX. The URL includes the server and port of the OPC server, for example, http://opcsvr:8080/xmlda/ for  a ClearSCADA server called 'opcsvr' on port 8080.
  UDP   123   NTP Servers   NTP Driver   The port is being used by the Network Time Protocol servers.

You can configure the NTP server by adjusting the NTP Server setting on the Scanner tab of the Scanner Form in ViewX. The protocol and port are fixed and cannot be re-configured.
  TCP   20876   Port Server   Drivers   The ports used for remote serial channels (dynamic ports). This is fixed and cannot be re-configured.

Each serial port will use a different TCP/IP port number.
  TCP   -   Port Server   Drivers and Third Party   The port for remote serial channels (static ports).

You can configure the static ports by editing the HKEY_LOCAL_MACHINE\SOFTWARE\Serck Controls\SCX6\PortServer/Ports registry key. The name of each value in the key is a port number.

For more information, see the Port Server documentation in the Server Administration Guide in ClearSCADA Help.
  TCP   0   Server   Telnet Clients   The ports used by the Telnet server for server monitoring. Each Telnet server will use a different port. The port that is currently being used is shown in the General\Information\Telnet Server section of the Server Status Tool.

You can configure the port by using the System Configuration\Logging\Server\Telnet Port setting on the Server Configuration Tool.

For more information, see the Server Administration Guide in ClearSCADA Help.
  TCP   0   Drivers   Telnet Clients   The ports used by the Telnet server for driver monitoring. Each Telnet server will use a different port. The port that is currently being used is shown in the Telnet Port column in the General/Modules section of the Server Status Tool.

You can configure the port by right-clicking on the individual driver in the General/Modules section of the Server Status Tool and then choosing the Logging option. This displays the Logging Configuration window. On the Configuration tab, you can change the port that is used by the driver by entering the required port number in the Telnet Port field.
  TCP   0   Drivers (Channels)   Telnet Clients   The port is used by the Telnet server for driver channel communications logging. The port that is currently being used in shown in the View window for the relevant channels.

You can configure the port by using the Enable Telnet pick action and entering the required port at the prompt. You can also define the port as a parameter for the EnableTelnet method.
  TCP   0   Port Server   Telnet Clients   The port is used by the Telnet server for port server logging. The port that is currently being used is shown in the header of log files.

You can configure the port by editing the HKEY_LOCAL_MACHINE\SOFTWARE\Serck Controls\SCX6\PortServer\LogTelnetPort registry key.

For more information, see the Port Server documentation in the Server Administration Guide in ClearSCADA Help.
  TCP   0   License Server   Telnet Clients   The port is used by the Telnet server for license server logging. The port that is currently being used is logged in the header of log files.

You can configure the port by editing the HKEY_LOCAL_MACHINE\SOFTWARE\Serck Controls\SCX6\LicenceServer\LogTelnetPort registry key.
  TCP   0   Alarm and Event Printer   Telnet Clients   The port is used by the Telnet server for OPC alarm and event printer logging. The port that is currently being used is shown in the header of log files.

You can configure the port by editing the HKEY_LOCAL_MACHINE\SOFTWARE\Serck Controls\SCX6\AEPrinter\LogTelnetPort registry key.



Notes



  • In this article, the term 'Telnet client' refers to any computer that is running a Telnet client application to access Geo SCADA diagnostics.
  • The term 'Drivers' refers to any driver that is installed on the ClearSCADA server except the internal drivers (Logic and QP - Query Processor).
  • The term 'Devices' refers to any SCADA device or application that accepts telemetry protocol via a network connection, for example:
  • Comtrol DeviceMaster
  • Port Server (Static Port)
  • The term 'Modbus TCP Master' refers to any master station (or similar) that has a Modbus TCP driver (including other ClearSCADA servers).
  • Port 0 means that this will be a dynamically assigned port (assigned by the operating system by default). You will need to configure and assign a specific port and then create a firewall rule for the port.
  • Where no port is specified, the port is configured in the database or registry by a user and there is no default setting.
  • Firewalls that support per program exceptions can be configured to unblock those Geo SCADA programs that require network access.


Go: Home Back

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore