Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

ClearSCADA 2017 R3 Upgrade Notes

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • ClearSCADA 2017 R3 Upgrade Notes
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 09:37 AM
0 Likes
0
1646
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 09:37 AM

ClearSCADA 2017 R3 Upgrade Notes

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 06:37 PM

📖 Home  Back  

Upgrading from ClearSCADA 2017 R1 and R2 Prior to June 2018



* Please be aware of all the issues covered in the above sections in addition to the following.*
  • There are changes to the ViewX startup configuration XML. This is because alarm banner settings can apply individually, so you can now have the alarm banner on any or all monitors. No change is needed if you are not using a customized ViewX startup configuration XML. A summary of the changes is here:


  • WindowContainers - The AlarmBannerWindow and AlarmBannerMode settings have been removed.

  • PrimaryWindowContainer and SecondaryWindowContainer

  • AlarmBannerDisplayState (new setting) - can be one of 'DockedTop', 'DockedBottom' or 'Fill'. Omit this to remove the alarm banner from this container.

  • AlarmBannerPersistSettings (new setting) - a boolean. This can only be specified as true for one window container. This causes the container where the setting is "true" to be the master for saving column size and order settings.


An example XML file for the June 2018 update onwards is shown here:



  • The WebX installer has been separated from the main installer in ClearSCADA 2017 R2, and is no longer triggered as a "follow-on" installation after ClearSCADA. As a result, the new IIS WebX has been promoted to a stand-alone option from the ClearSCADA 2017 R2 installation main menu screen.


  • Security certificates for the web server -- please refer to the File: Release Notes (See links below) for 2017 R2.


  • ViewX startup configuration changes. The format has changed -- please see the Release Notes and product help to understand what you need to do. The keyword "CanFloatWindows" has been added and the keywords "InterfaceMode" and "IsRestrictedWorkstation" have been removed.


Upgrading ClearSCADA Mobile


Between ClearSCADA 2017 and ClearSCADA 2017 R2 the location of the Mobile Settings database changed.
Therefore upgrading from a version of ClearSCADA Mobile at or before ClearSCADA 2017 will require your action.
You will need to move your database (.sdf file) from:
C:\ProgramData\Schneider Electric\ClearSCADA Mobile

to
C:\ProgramData\Schneider Electric\ClearSCADA



Upgrading from ClearSCADA 2015 R2.x



* Please be aware of all the issues covered in the above sections in addition to the following.*
  • To reinforce implementation of best practice security, the Super User now enforces a 12-character password to discourage extended use when a local Administrator User Account object should be used instead. If the existence of a Super User account is detected on upgrade to ClearSCADA 2017, you will be asked to enter new credentials to comply with increased password strength.


  • New options have been added within Server Configuration Tool to control the state of the Wonderware Alarm Provider (WWAP). This new option defaults to False on upgrade to ClearSCADA 2017 and therefore should be enabled (and then the server restarted) if the Alarm Provider is in use. Existing ClearSCADA users that wish to continue to use the WWAP service, it is recommended that immediately after upgrade to ClearSCADA 2017 the WWAP service is enabled via the Server Configuration Tool, and the ClearSCADA server restarted to avoid loss of cached alarms.


  • The ClearSCADA Mobile Companion installation was bundled with the new WebX installer for ClearSCADA 2015 R1 and 2015 R2. The bundling of the Mobile Companion and WebX installation has been reversed in ClearSCADA 2017, such that the Mobile Companion is now a separate feature that can be selected during installation of the ClearSCADA Server.


  • A new limit has been applied to IIS WebX which, by default, restricts the Alarm Banner display to list only the top 100 entries. When alarms are not able to be shown due to the above restriction, an entry is added to the bottom of the Alarm Banner list stating that "Maximum alarms for WebX shown", followed by a count of the alarms that are not visible. The default limit of 100 should be suitable for most users, although can be increased by adjusting the "MaxAlarms" WebX Application Setting within IIS Manager.


  • In this version the License Server for client licensing (plus Port Server and AEPrinter services) use virtual accounts. The "NT SERVICE\ALL SERVICES" account should be assigned the "Log on as a service" user right, see https://technet.microsoft.com/en-us/library/cc794944(v=ws.10).aspx for details on how to do this. Virtual accounts will not work without this. If this is not configured, an error will be shown in the Windows system logs. This virtual user also will needs to be granted permissions to read the directory where the license file is stored, if applicable.


Upgrading from ClearSCADA 2015 R1.x



Please be aware of all the issues covered in the above sections in addition to the following.


  • The installation of ClearSCADA Mobile and WebX has been separated in ClearSCADA 2015 R2 to provide a simplified upgrade experience. The WebX installation will be executed after successful installation of ClearSCADA 2015 R2, whereas the installation of ClearSCADA Mobile will need to be manually executed if required via the link on the ClearSCADA installation Splash Screen.

Existing installations of ClearSCADA 2015 R1 Web and Mobile will first need to be uninstalled prior to installation of ClearSCADA 2015 R2. The re-installation of WebX after installation of ClearSCADA 2015 R2 will need to manually re-configure any non-default ports, as these will not be remembered from the previous WebX installation. Mobile users running versions prior to ClearSCADA 2015 R1 should be able to upgrade to ClearSCADA 2015 R2 without first uninstalling ClearSCADA Mobile.

  • ClearSCADA 2015 R2 enforces new restrictions during upgrade to prevent inadvertently upgrading to an older ClearSCADA version which could have unexpected consequences.

For example, an upgrade from ClearSCADA 2013 R1.2 (73.4955) to ClearSCADA 2013 R2 (74.5094) is valid because 5094 > 4955. In comparison, an upgrade from ClearSCADA 2013 R2.2 (74.5700) to ClearSCADA 2014 R1 (75.5210) is not recommended because 5210 < 5700, even though it is an increase in the minor version number, as this may reintroduce bugs that have been fixed in the later version.
ClearSCADA should only be upgraded to a newer version that has a higher build number than the currently installed version.

Upgrading from ClearSCADA 2014 R1.x



Please be aware of all the issues covered in the above sections in addition to the following.


  • The ClearSCADA Sample Database now appears as two "Configuration Samples" options within a custom ClearSCADA installation to allow users the choice of whether or not this is installed. At completion of the ClearSCADA installation, there is no longer a Demonstration Modules installer to launch the Database and install the Configuration Samples. Instead, when the Configuration Samples are selected for installation (included within a "Full" installation) the Sample Database will automatically be loaded when the ClearSCADA server is started if an existing database is not found.


  • Prior to upgrading the user needs to stop the ClearSCADA mobile companion service using the ClearSCADA Service Manager tool.


  • Creation of a ClearSCADA Super User account is now mandatory during installation in order to provide administration access to configure new Example User Accounts. It is strongly recommended that this is disabled via the System Configuration utility once a replacement Administrator user account has been created within the database.


  • The built-in Super User account, if enabled, is only valid on the local ClearSCADA server machine, and will be denied access to ClearSCADA if logon is attempted from a remote client machine.


  • A new database table, called DBDictionary, has been created to store the translation strings for each dictionary language as required by the user. Each entry within this table specifies the Dictionary Name (or Language), a Search String, a Replacement String, and an optional Comment. When configured, users who have their Locale set to match one of the Dictionary Languages would see the Replacement String used in place of a Search String if it were to appear on a mimic.

  • Enabling the dictionary functionality as described above will disable translation using any existing Dictionary Files. In this case, migration of these existing files to the new dictionary table is necessary to provide continued translation.

  • Translation of strings using the string dictionary only works for whole strings. Strings on mimics cannot be built from multiple translated strings. A new "translate()" function has been created for use within server expressions, client expressions, scripting and SQL syntax to allow multiple separate strings to be translated and concatenated together. An example mimic text animation could include:Translate('@This section of string is translated') + ' but this section is not.'


Upgrading from ClearSCADA 2013 R2.x



Please be aware of all the issues covered in the above sections in addition to the following.
  • ClearSCADA software previously had an option of an integrated Kepware Technologies KEPServerEX4 PLC driver; however with the evolution of ClearSCADA this integrated PLC driver suite previously is no longer available within ClearSCADA 2014 R1 or future versions. To ensure the continuous, long-term operation of your system we recommend that you migrate to an external installation of KepServerEX5 (Kepware's latest version) prior to the upgrade to ClearSCADA 2014 R1. This migration will require the conversion of any existing PLC database objects into corresponding OPC database objects, for which a documented procedure and software tool has been prepared and will be provided free of charge from Schneider Electric on request. An upgrade to ClearSCADA 2014 R1 should be performed only after all PLC database objects have been migrated to corresponding OPC database objects.


Go: Home Back
  • Tags:
  • SCADA Innovation

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore