Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

ClearSCADA 2014 R1.1 Upgrade Notes - ViewX Client

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • ClearSCADA 2014 R1.1 Upgrade Notes - ViewX Client
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 10:37 AM
0 Likes
0
749
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 10:37 AM

ClearSCADA 2014 R1.1 Upgrade Notes - ViewX Client

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 07:37 PM

📖 Home  Back  
Please read the information below prior to upgrading to SCADA Expert ClearSCADA 2014 R1.1 for important information regarding changes to the ViewX User Interface in this version.

Migrating your Multi-Head Implementation



Support for multiple monitors has been completely redesigned to enhance the level of functionality and improve the user experience, however this has resulted in changes to the way this is implemented within the new ViewX client. The previous "multi-head" approach provided the capabilities of both multiple independent instances (each with potentially separate database connections), as well as multi-monitor installations (where the same database connection was shared among all heads), however these two scenarios need to be handled separately. Please refer to the relevant section below for details.

Single Instance of ViewX with Multiple Monitors



A multi-monitor configuration of ViewX was implemented using a combination of the following command-line options:
  Old Command Line Option   Description
  "/head:"   Invokes a separate ViewX instance called 'n'
  "/logonHead:"   Automatic logon to the instance(s) specified by 'n'
  "/navigateOnHead:"   Displays documents on the instance specified by 'n'
  "/navigateSingleWindowOnHead:"   Displays documents on the instance specified by 'n' in the active window if possible
  "SCX://///"   Displays specified document


This configuration has been replaced using the new multi-monitor functionality available within ClearSCADA 2014 R1.1, and the implementation within your system should be updated to align with the new functionality available. The following examples should provide guidance for this conversion process. For more information please refer to the ClearSCADA Online Help under: Core Reference > Client Administration > Client Administration Guide - Launch a ViewX Client on a Multi-Monitor Setup.

Example 1 : Dual-Monitors with Full-Screen Alarm Banner



In this scenario the system would be configured a dual-head client, with one screen displaying a Full Screen Alarm Banner. The previous implementation could have been similar to the following:
"C:\Program Files
 (x86)
\Schneider Electric\ClearSCADA\ViewX.exe /head:1 /navigateOnHead:2 /SCX:///*/AlarmList"


An equivalent implementation could be as follows:
"C:\Program Files (x86)\Schneider Electric\ClearSCADA\SE.Scada.ViewX.exe /startup:C:\ClearSCADAStartup\DualMonAlarm.xml"


Where "DualMonAlarm.xml" is as follows:


                  Overview  


Example 2 : Triple Monitors



In this scenario the system would be configured a simple triple-head client. The previous implementation could have been similar to the following:
"C:\Program Files
 (x86)
\Schneider Electric\ClearSCADA\ViewX.exe /head:1 /logOnHead:2,3"


An equivalent implementation could be as follows:
"C:\Program Files (x86)\Schneider Electric\ClearSCADA\SE.Scada.ViewX.exe /startup:C:\ClearSCADAStartup\TripleMon.xml"


Where "TripleMon.xml" is as follows:


                      Overview    Eastern Region.Zone 1.Plant Overview    Eastern Region.Zone 2.Plant Overview  


Multiple Independent ViewX Instances



Previously this scenario was implemented using the following command-line switches:
  No.   * Old Command Line Option*
  New Command Line Option   Description
  1   "/head:"   "/instance:"   Invokes a separate ViewX instance called 'n'
  2   "/systems:"     Specifies systems' xml connection file




The "/head:" command line option has been replaced with the new "/instance:" command, and provides equivalent functionality. The previous restriction of 5 concurrent heads (via configuration of "n" as numbers 1 through 5) has been removed.

The "/systems:" command line option remains unchanged.

Example : Two Instances with Separate Systems Connection


In this scenario two separate instances of the client with be launched, with each connecting to a different system(s). The previous implementation could have been similar to the following:

Head 1:
"C:\Program Files
 (x86)
\Schneider Electric\ClearSCADA\ViewX.exe"

Head 2:
"C:\Program Files
 (x86)
\Schneider Electric\ClearSCADA\ViewX.exe" /head:2 /systems:C:\ClearSCADAStartup\Systems.xml"





An equivalent implementation could be as follows:

Head 1:
"C:\Program Files (x86)\Schneider Electric\ClearSCADA\SE.Scada.ViewX.exe"

Head 2:
"C:\Program Files (x86)\Schneider Electric\ClearSCADA\SE.Scada.ViewX.exe" /instance:2 /systems:C:\ClearSCADAStartup\Systems.xml"


Go: Home Back
  • Tags:
  • SCADA Innovation

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore