Improved the server redundancy support so that ClearSCADA 2007 R1.1 servers can synchronize with ClearSCADA 2007 R0 servers. This allows for a seamlessupgrade procedure from ClearSCADA 2007 R0.
Corrected the problem of scripted mimic menus appearing on the wrong screen on multi-monitor systems.
Fixed a memory leak in ViewX when switching between mimics containing large numbers of polylines.
Corrected template instance conversion for RealFLO points to ensure 6 digit addressing is handled.
Corrected a problem that disallowed spaces from system names.
DNP3 SCADAPack ES configuration download has been corrected to send the correct network configuration parameters.
Fixed a potential server crash that could occur if a web request is received with an unrealistically large value in the Content-Length header field.
Fixed a potential server crash that could occur if the total number of OPC DA groups created exceeded 9999.
Corrected the OPC DA Client Driver to pass an empty string for the AccessPath parameter of each tag. Previously the driver passed a NULL pointer, which caused the operation with some OPC DA servers to fail.
Fixed a problem where correctly configured Modbus points would not update an report bad quality. This problem occurred if the Modbus driver was scanning a slave device via TCP and the configured scan period was greater than the slave device timeout.