I want to use the Com'x 510 to connect the PM5310 METER, i create the new device pm5310 , but i want to log the individual voltage and current harmonic , but can't show this item , just THD.
so, i go to create the custom libary , i find the pm5310 individual mapping address and create . but commucation always error.
someone can help me please. thanks
Link copied. Please paste this link to share this article on your social media post.
Hi,
When creating a custom model, you need to enter the Modbus address, not the Modbus register. The Modbus address is the Modbus register - 1.
I hope this helps.
Randi
Link copied. Please paste this link to share this article on your social media post.
Hi Randi:
thanks , but i use the dignostic funtion read the register , for the example , i want to read PM5310 A-N voltage THD ,Register is 21330 , the individual it can be read sucessful , no problem
but i create the custom library , i modify the frame , start address , you means i should key in 21329 (21330-1) , maybe works right ?
Link copied. Please paste this link to share this article on your social media post.
Hello @gibson_huang_ep
I confirm. Register = Modbus Address + 1
For PM5300 serie, THD Voltage A-N register is 21330.
The embedded Diagnostic Tool of the Com'X is working with the Register number. So in this case if you read 21330 you will have a goof value.
But if you want to create a Custom Model (for any device) => you need to enter the Modbus Address of the Register (and not the register itself).
A Modbus Frame is always composed of the Address of the Register.
A good example is to create your PM5310 Model based on the Existing PM5320 Model. you will see the differences.
Regards,
Romain
Link copied. Please paste this link to share this article on your social media post.
Hi @Romain_Polette :
thanks for the useful reply , i can use cutom library to read the modbus address , but the value is weird, in that time nornally the VTHD a-n is between 18%-30% , but the com'x 510 show -2695,977,546,809,344,00 , as the picture as below.
please teach me , how to adujust the parameter to display correct value . thanks again.