com'x 510 and PM5310 individual harmonic logging Question

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • com'x 510 and PM5310 individual harmonic logging Question
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
96
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
41
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
gibson_huang_ep
Lieutenant | EcoXpert Master gibson_huang_ep Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-12-11 04:05 AM

0 Likes
4
1017
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-11 04:05 AM

com'x 510 and PM5310 individual harmonic logging Question

I want to use the Com'x 510 to connect the PM5310 METER, i create the new device pm5310 , but  i want to log the individual voltage and  current harmonic , but  can't show this item , just THD.

 

so, i go to create the custom libary , i find the pm5310 individual mapping address and create . but commucation always error. 

 

someone can help me please. thanks

Tags (2)
  • Tags:
  • com'x 510
  • pm5310
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2019-12-11 05:24 AM

0 Likes
3
1014
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-11 05:24 AM

Hi,

 

When creating a custom model, you need to enter the Modbus address, not the Modbus register.  The Modbus address is the Modbus register - 1.

 

I hope this helps.

 

Randi

Reply
gibson_huang_ep
Lieutenant | EcoXpert Master gibson_huang_ep Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-12-11 06:30 AM

0 Likes
2
1012
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-11 06:30 AM

Hi Randi:

 

thanks , but i use the dignostic funtion  read the register ,  for the example , i want to read PM5310 A-N voltage THD ,Register is 21330 , the individual it can be read sucessful , no problem

 

but  i create the custom library , i modify the frame , start address , you means i should key in  21329 (21330-1) , maybe works right ?  

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2019-12-11 06:57 AM

0 Likes
1
1008
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-11 06:57 AM

Hello @gibson_huang_ep 

 

I confirm. Register = Modbus Address + 1

 

For PM5300 serie, THD  Voltage A-N register is 21330.

 

The embedded Diagnostic Tool of the Com'X is working with the Register number. So in this case if you read 21330 you will have a goof value.

But if you want to create a Custom Model (for any device) => you need to enter the Modbus Address of the Register (and not the register itself).

 

A Modbus Frame is always composed of the Address of the Register. 

 

A good example is to create your PM5310 Model based on the Existing PM5320 Model. you will see the differences.

 

Regards,

 

Romain

Romain POLETTE
Solution Architect - France Operations
Attachments
Reply
gibson_huang_ep
Lieutenant | EcoXpert Master gibson_huang_ep Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-12-16 07:28 AM

0 Likes
0
1003
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-12-16 07:28 AM

Hi @Romain_Polette :

 

thanks for the useful reply , i can use cutom library to read the modbus address , but the value is weird, in that time nornally the VTHD a-n is between 18%-30% , but the com'x 510 show -2695,977,546,809,344,00 , as the picture as below.

 

please  teach  me , how to adujust the parameter to display correct value . thanks again.

 

 

comx510_PM5310_VTHD issue.jpg

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of