Hi Arief,
This is possible, but would be extremely slow to load the ComX interface over a 2G connection. There are a couple of other considerations that may make this very difficult in practice:
Many cellular networks will block this traffic automatically
Unless you have paid for a static IP address sim card from the provider, the IP address of the ComX on the cellular network may be frequently changing
Make sure you've enabled HTTP over GPRS in the firewall settings page.