Both units have webserver built in. I would like to know what the difference on the webpages based on the dashboard. What is the pro and cons between the hardware and the webserver?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello,
Would prefer to say that PAS800 is an energy server with capability to log data and display or export logged data.
PAS600 is much more a gateway ( cloud gateway as example) with data retention in case of communication issues. When data are pushed, they are deleted from the memory.
If we can compare PAS and COMX ( which is not the case), PAS600 ~ COMX210 and PAS800 ~ COMX510.
Link copied. Please paste this link to share this article on your social media post.
Hi Thierry,
What will be the pro and con for the built in webserver? Is there any difference?
Link copied. Please paste this link to share this article on your social media post.
hello,
I do not kbnow what you call the built in webserver, in term of Configuration pages no difference, but normally PAS800 shall be able to replace 510 which has the capability to build embeded web dashboard to display data which is not available today with 1.5 for PAS.
If you want modbus gateway => no difference
If you want a cloud gateway => no difference, prefer PAS600
If you need local energy server or the ability to push csv to SFTP yopu have to use PAS800
If you need PoE => you have to make a choice
Link copied. Please paste this link to share this article on your social media post.
I am referring to the built in GUI if i choose to use the PAS600L or PAS800L locally instead of cloud base like facility expert or energy hub.
Link copied. Please paste this link to share this article on your social media post.
Hi Derrick,
If the need is to use a Panel Server in standalone mode without BMS, SCADA or advisor (FE, Energy Hub), I advise you to use PAS800.
PAS600 web page offer the possibility to view ONLY real time measurement
PAS800 web page offer the possibility to view real time measurement +TRENDS (recorded value)
Your previous screenshot was an example of real time measurement in PAS600.
I add bellow a screenshot of trend from PAS800
Link copied. Please paste this link to share this article on your social media post.
Hi Thierry,
Thanks for the explanation.
I have a question on the dashboard that i saw it on the website.
I cannot see the equipment, notification and team at your image that you attached to me previously.
Link copied. Please paste this link to share this article on your social media post.
a question, if I have 2 PAS600 and I insert a PAS800 can I use the "trand" function also for the devices connected to the two PAS600? thanks
Link copied. Please paste this link to share this article on your social media post.
hello @TecnoEmanuele
As soon as devices are added in PAS800 (using virtual ID from PAS600) and data logging or sampling is configured on PAS800 you will be able to use the historical data (datalogger).
When one PAS is having devices connected on a another PAS this PAS is called the Child gateway
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
thanks for the information. then I will proceed with the purchase. in case of problems with the configuration I will come back to you. 😉
thanks