What is the best way to connect a temperature sensor to an EGX300?

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • What is the best way to connect a temperature sensor to an EGX300?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
maxencevanhove
maxencevanhove Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-01-03 03:47 AM

0 Likes
6
1784
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-01-03 03:47 AM

What is the best way to connect a temperature sensor to an EGX300?

Hi there,

One of my customers asked me how to collect a temperature sensor to an already installed EGX300?

Do you have any recommendation?

Thanks in anticipation!

-Maxence

Tags (4)
  • Tags:
  • egx300
  • sensor
  • sim10
  • temperature
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2014-01-08 08:33 AM

2 Likes
0
1630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-01-08 08:33 AM

Hello Maxence,

If the temperature sensor is capable of communicating via Modbus, you can connect the sensor on the EGX300's RS-485 serial port.  You can then create a custom device type using the Custom Device Type Generator to view and log data from this device.

Randi

Reply
LaurentCoene
Captain LaurentCoene Captain
Captain

Posted: ‎2014-01-14 01:04 AM

0 Likes
1
1630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-01-14 01:04 AM

Hi Maxou!

Many ways to do that and it really depends on the temperature sensor. If it is Modbus like the CWLP from Veris, use the custom device type generator and you're done. Only problem with that is that Modbus temperature sensors are typically a little more expensive.

If you have a 0-10V. or a 4-20mA, you will need some sort of Modbus converter in between. For example, you can use the AI (Analog Input) of the SIM10M as described here. However it can get messy/tricky.

Frankly speaking, taking cost into consideration, I would replace the EGX300 by a Com'X200 which has two Analog Inputs. You can wire your 0-10 or 4-20 directly in, and you're done!

If you have many many sensors, then you should look at using some stuff from the building BU (maybe using the GW and EnOcean sensors....)...

Anyway, hope this helps!

Reply
dborle
dborle Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-01-14 04:25 AM

0 Likes
0
1630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-01-14 04:25 AM

Hi Laurent,

I agree with you. But it also depends, whether Maxence needs the capability of the EGX300 to show realtime data and logged data over the integrated web server or not (as the Com'X doesn't has this capability).

Cheers

Daniel

Reply
josgrafe
Lieutenant JG josgrafe
Lieutenant JG

Posted: ‎2014-02-01 02:43 AM

0 Likes
0
1630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-01 02:43 AM

We have connected an 0-10V sensor via a SIM10 module.

Reply
sesa205726_brid
Lieutenant JG sesa205726_brid Lieutenant JG
Lieutenant JG

Posted: ‎2014-02-05 01:37 AM

0 Likes
0
1630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-05 01:37 AM

In Italy, we have connected a temperature sensor to SIM10M. There are two way for to connect the temperature sensor to analog input of SIM10M. The features of the analog input of SIM10M are:

0-10 V with resolution of 0.01.

The featuring of the analog input implies two possible connection between devices:

1. if you use a PT100 you need a Crouzet convert to convert the current signal of the sensor in the corresponding voltage signal;

2. if you use a sensor with output directly in voltage, you can connect this one to analog input of SIM10M.

By

Reply
conchimunoz
conchimunoz Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-02-05 04:23 AM

0 Likes
0
1630
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-02-05 04:23 AM

Hi!

We did this configuration before and we choose an OTB. OTB is a I/O distributed device  which can communicate in ModBus protocol and you can add on it a card for analog inputs  (4-20ma, 0-10v, pt100, pt1000, etc..). Then, in the EGX300, you can configure a custom device to communicate with the OTB.

You can read more information about Modbus OTB in this link:

http://www2.schneider-electric.com/documents/electrical-distribution/en/shared/interactive-catalogue...

I hope it helps.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore