Updated old version firmware Acti 9 Smartlink SI D

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Updated old version firmware Acti 9 Smartlink SI D
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
96
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
41
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
KCWong
Lieutenant JG KCWong Lieutenant JG
Lieutenant JG

Posted: ‎2020-05-20 11:36 PM

0 Likes
3
1390
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-20 11:36 PM

Updated old version firmware Acti 9 Smartlink SI D

Hi Expert,

 

1. I have 3 pcs of A9XMWA20 with firmware v1.2.1 and v2.1. How can I update to latest firmware? I have installed EcoStruxure Power Commission software but still failed(min. requirement is v2.3).

 

2. I have some powtag A9MEM1522 & 1520 that have connected to another old SI-D before. However the old SI-D failed. When I want to connect those powertag to new SI-D, they cannot scan by the new SI-D and the red led are fast blinking. How can reset the powertag to join to the new SI-D?

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
KCWong
Lieutenant JG KCWong Lieutenant JG
Lieutenant JG

Posted: ‎2020-06-08 09:01 PM

1 Like
1
1375
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-08 09:01 PM

Hi Nedjma,

 

I have solve those problem when I reinstall the EcoStruxure Power Commission again.

See Answer In Context

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2020-06-08 11:22 PM

1 Like
0
1373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-08 11:22 PM

Hello @KCWong ,

 

Good to know you have solved your issue.
Please keep in mind that you need to connect you SID directly to EPC if you want to upgrade your Smartlink FW.

If you upgrade through some network routers, you will fail your upgrade.

 

It is important that EPC and the Smartlink are located on the same sub-network.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 3
Anonymous user
Not applicable

Posted: ‎2020-06-08 01:25 AM

0 Likes
2
1378
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-08 01:25 AM

Hi the community members can you help this member on this topic, please?

 

@Romain_Polette do you think you can advise on this topic?

@KCWong if you still in the same situation please do not hesitate to inform us here.

 

Have a nice day.

 

Reply
KCWong
Lieutenant JG KCWong Lieutenant JG
Lieutenant JG

Posted: ‎2020-06-08 09:01 PM

1 Like
1
1376
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-08 09:01 PM

Hi Nedjma,

 

I have solve those problem when I reinstall the EcoStruxure Power Commission again.

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2020-06-08 11:22 PM

1 Like
0
1374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-06-08 11:22 PM

Hello @KCWong ,

 

Good to know you have solved your issue.
Please keep in mind that you need to connect you SID directly to EPC if you want to upgrade your Smartlink FW.

If you upgrade through some network routers, you will fail your upgrade.

 

It is important that EPC and the Smartlink are located on the same sub-network.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of