Hi Expert,
1. I have 3 pcs of A9XMWA20 with firmware v1.2.1 and v2.1. How can I update to latest firmware? I have installed EcoStruxure Power Commission software but still failed(min. requirement is v2.3).
2. I have some powtag A9MEM1522 & 1520 that have connected to another old SI-D before. However the old SI-D failed. When I want to connect those powertag to new SI-D, they cannot scan by the new SI-D and the red led are fast blinking. How can reset the powertag to join to the new SI-D?
Link copied. Please paste this link to share this article on your social media post.
Hi Nedjma,
I have solve those problem when I reinstall the EcoStruxure Power Commission again.
Link copied. Please paste this link to share this article on your social media post.
Hello @KCWong ,
Good to know you have solved your issue.
Please keep in mind that you need to connect you SID directly to EPC if you want to upgrade your Smartlink FW.
If you upgrade through some network routers, you will fail your upgrade.
It is important that EPC and the Smartlink are located on the same sub-network.
Regards,
Posted: 2020-06-08 01:25 AM
Link copied. Please paste this link to share this article on your social media post.
Hi the community members can you help this member on this topic, please?
@Romain_Polette do you think you can advise on this topic?
@KCWong if you still in the same situation please do not hesitate to inform us here.
Have a nice day.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello @KCWong ,
Good to know you have solved your issue.
Please keep in mind that you need to connect you SID directly to EPC if you want to upgrade your Smartlink FW.
If you upgrade through some network routers, you will fail your upgrade.
It is important that EPC and the Smartlink are located on the same sub-network.
Regards,