Un-Binding PowerTag

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Un-Binding PowerTag
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
PowerLogic™ PowerTag

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Mark_Raftery
Ensign Mark_Raftery Ensign
Ensign

Posted: ‎2022-08-02 07:11 AM

1 Like
5
3166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-02 07:11 AM

Un-Binding PowerTag

Hi,

 

I have a system that had seven A9MEM1520 bound to an Acti 9 Smartlink SI D

Unfortunately the Smartlink has catastrophically failed and I would like to replace this unit with a PaS600.

I have removed one of the PowerTags' and tried in vain to connect to my PaS.

I have a new A9MEM1520, which the PaS will detect.

I belive that the PowerTag is bound to the old Smartlink and that is why the PaS cannot discover it.

 

Is there a way of resetting this old PowerTag so that it can be discovered?

 

A9MEM1520

3N-2017-W44-5

0051

V315

 

Kind regards from Mark

  • Thumbnail of PowerLogic™ PowerTag
    Schneider Electric
    PowerLogic™ PowerTag
View products (1)
Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-08-18 05:16 AM

0 Likes
4
3031
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-18 05:16 AM

Hi Mark,

 

After crash of the SID , the A9MEM15020 should fast blink red to indicate that there are in the communication loss.

At this step , a power cyle of the PowerTag offers a recovery mode to switch in discovery mode (for a limited time of X minutes). After the power cycle, the PowerTag should bling orange to indicate the discovery mode.

 

So can you confirm that the PowerTag blink orange when you launch the discovery mode on the PAS600 ?  

 

Then; as you mention, there is perhaps a problem of fw compatibility between the PAS600 and the powerTag.

I can ask information for the compatibility between the PAS and the PowerTag ) if you share  a photo of the  PowerTag sticker (fw version is printed on it => exemple hereunder)

Can you please send a photo ?

We keep in touch.

 

PowerTag fw version.jpg

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 5
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-08-18 05:16 AM

0 Likes
4
3032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-18 05:16 AM

Hi Mark,

 

After crash of the SID , the A9MEM15020 should fast blink red to indicate that there are in the communication loss.

At this step , a power cyle of the PowerTag offers a recovery mode to switch in discovery mode (for a limited time of X minutes). After the power cycle, the PowerTag should bling orange to indicate the discovery mode.

 

So can you confirm that the PowerTag blink orange when you launch the discovery mode on the PAS600 ?  

 

Then; as you mention, there is perhaps a problem of fw compatibility between the PAS600 and the powerTag.

I can ask information for the compatibility between the PAS and the PowerTag ) if you share  a photo of the  PowerTag sticker (fw version is printed on it => exemple hereunder)

Can you please send a photo ?

We keep in touch.

 

PowerTag fw version.jpg

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
Mark_Raftery
Ensign Mark_Raftery Ensign
Ensign

Posted: ‎2022-08-31 12:00 AM

0 Likes
3
2922
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-08-31 12:00 AM

Good morning Thierry

I have just got back from PTO.

Thank you for your reply, I will take photo and try what you have sugested and let you know the outcome in the coming days.

KRF Mark

Tags (1)
  • Tags:
  • english
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-09-02 02:30 AM

0 Likes
2
2885
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-02 02:30 AM

Hello Mark,

 

I complete my previous answer:

if your refer to the last Panel Server release note (https://www.se.com/ww/en/download/document/DOCA0178EN/ )

Panel Server support PowerTag Energy Sensors 63 Amps with  firmware version 4.0.429 or higher

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
Mark_Raftery
Ensign Mark_Raftery Ensign
Ensign

Posted: ‎2022-09-29 11:36 PM

0 Likes
1
2629
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-29 11:36 PM

Good morning @Thierry_Baudard ,

Sorry this has taken a long time to respond, I had some SE Priorities.

I am pleased to let you know that the instructions on the re binding to the new PaS600L worked and it is now bound to the PaS.

I have attached a photo of the unit, but details of unit. 3N-2017-W44-5  0051  V315

Thank you for your support

 

Attachments
Tags (1)
  • Tags:
  • english
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-09-30 12:36 AM

0 Likes
0
2622
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-30 12:36 AM

Hello Mark,

 

Thanks for your positive feedback and no problem for the delay (Customer First !)

 

If this post help you to solve the problem, you can tag it as a solution to help other community member to identify this post.

 

Best regards 

 

 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore