ULP Systems

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • ULP Systems
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
106
Guillaume_Evrard
Commander Guillaume_Evrard Commander
47
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
31
View All
Related Products
product field
Schneider Electric
MasterPact MTZ

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
jedzruiz1985
Lieutenant JG jedzruiz1985
Lieutenant JG

Posted: ‎2025-07-23 04:20 PM

0 Likes
2
46
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 04:20 PM

ULP Systems

Hi Xperts,

 

Just want to confirm, if multiple ACBs (MTZ) have their own IFM stacked to an IFE server (daisy chained via stacking connectors),  do we still need to provide separate 24VDC on each ULP module of the breakers even though the IFM is providing 24V already from the IFE Server thru the IFMs?

 

Thanks in advance,

 

Jiedan

  • Thumbnail of MasterPact MTZ
    Schneider Electric
    MasterPact MTZ
View products (1)
Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-07-23 09:03 PM

0 Likes
0
39
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 09:03 PM

Hello @jedzruiz1985 

For MTZ I would say that the 24VDC connector is feeding the communication but also the Micrologic. You are right that stacking connector is feeding the IFM. For Masterpact NT/NW you do not need to have separated PSU for BCM ULP but for MTZ yes it is mandatory as per ULP manual:

Guillaume_Evrard_0-1753329787043.png

 

Kind Regards

See Answer In Context

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-07-24 05:52 AM

0 Likes
0
26
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-24 05:52 AM

Hello @jedzruiz1985 , 

 

Please refer to the Micrologic X User Guide to better know how this trip unit is power supplied:

 

According to this section of the ULP Guide:

The ULP port module:

  • Supplies power to the MicroLogic X control unit.
  • Has an integrated ULP line termination.
  • Enables the connection to external ULP modules, like the IO module or the IFE interface.

For MasterPacT MTZ drawout circuit breakers with optional EIFE interface, the ULP port module:

  • Supplies power to the EIFE interface.
  • Connects the EIFE interface to the other IMU modules (for example, IO module).

There is a dedicated ULP Power Supply section in the ULP guide:

  • ULP port module for MasterPacT MTZ circuit breakers => Must be connected to a 24 Vdc power supply and cannot be powered through its ULP port.
  • IFE Ethernet switchboard server => Must be connected to a 24 Vdc power supply and cannot be powered through its ULP port.
  • IFM Modbus-SL interface for one circuit breaker => Must be connected to a 24 Vdc power supply and cannot be powered through its ULP port.

Tl;dr:

  • MTZ ULP port must be supplied by 24DC
  • IFE must be powered by 24DC
  • You can stack up to 11 IFM to an IFE

 Regards, 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 2
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-07-23 09:03 PM

0 Likes
0
40
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-23 09:03 PM

Hello @jedzruiz1985 

For MTZ I would say that the 24VDC connector is feeding the communication but also the Micrologic. You are right that stacking connector is feeding the IFM. For Masterpact NT/NW you do not need to have separated PSU for BCM ULP but for MTZ yes it is mandatory as per ULP manual:

Guillaume_Evrard_0-1753329787043.png

 

Kind Regards

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-07-24 05:52 AM

0 Likes
0
27
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-24 05:52 AM

Hello @jedzruiz1985 , 

 

Please refer to the Micrologic X User Guide to better know how this trip unit is power supplied:

 

According to this section of the ULP Guide:

The ULP port module:

  • Supplies power to the MicroLogic X control unit.
  • Has an integrated ULP line termination.
  • Enables the connection to external ULP modules, like the IO module or the IFE interface.

For MasterPacT MTZ drawout circuit breakers with optional EIFE interface, the ULP port module:

  • Supplies power to the EIFE interface.
  • Connects the EIFE interface to the other IMU modules (for example, IO module).

There is a dedicated ULP Power Supply section in the ULP guide:

  • ULP port module for MasterPacT MTZ circuit breakers => Must be connected to a 24 Vdc power supply and cannot be powered through its ULP port.
  • IFE Ethernet switchboard server => Must be connected to a 24 Vdc power supply and cannot be powered through its ULP port.
  • IFM Modbus-SL interface for one circuit breaker => Must be connected to a 24 Vdc power supply and cannot be powered through its ULP port.

Tl;dr:

  • MTZ ULP port must be supplied by 24DC
  • IFE must be powered by 24DC
  • You can stack up to 11 IFM to an IFE

 Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of