Hi Xperts,
Just want to confirm, if multiple ACBs (MTZ) have their own IFM stacked to an IFE server (daisy chained via stacking connectors), do we still need to provide separate 24VDC on each ULP module of the breakers even though the IFM is providing 24V already from the IFE Server thru the IFMs?
Thanks in advance,
Jiedan
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985
For MTZ I would say that the 24VDC connector is feeding the communication but also the Micrologic. You are right that stacking connector is feeding the IFM. For Masterpact NT/NW you do not need to have separated PSU for BCM ULP but for MTZ yes it is mandatory as per ULP manual:
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985 ,
Please refer to the Micrologic X User Guide to better know how this trip unit is power supplied:
According to this section of the ULP Guide:
The ULP port module:
For MasterPacT MTZ drawout circuit breakers with optional EIFE interface, the ULP port module:
There is a dedicated ULP Power Supply section in the ULP guide:
Tl;dr:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985
For MTZ I would say that the 24VDC connector is feeding the communication but also the Micrologic. You are right that stacking connector is feeding the IFM. For Masterpact NT/NW you do not need to have separated PSU for BCM ULP but for MTZ yes it is mandatory as per ULP manual:
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985 ,
Please refer to the Micrologic X User Guide to better know how this trip unit is power supplied:
According to this section of the ULP Guide:
The ULP port module:
For MasterPacT MTZ drawout circuit breakers with optional EIFE interface, the ULP port module:
There is a dedicated ULP Power Supply section in the ULP guide:
Tl;dr:
Regards,