Hello,
I would like to know if it's possible to read the inputs of the comX510 with an internal registers?
I have a Pt100 connected to my ComX510 and I would like to read the temperature with PME and I can't find any information about a modbus register where I can read those values.
Do you have any informations about this point?
Thanks
Posted: 2017-01-23 08:58 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Jean-Pierre,
Yes, it is possible to read the values in the registers of the ComX itself. Please see the Communication Settings section of the User Manual, in the subsection Accessing the Internal Modbus Slave Device. Appendix F in the User Manual lays out the register map. Here is a link to the User Manual.
Best Regards,
Colton Peltier
Posted: 2017-01-23 08:58 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Jean-Pierre,
Yes, it is possible to read the values in the registers of the ComX itself. Please see the Communication Settings section of the User Manual, in the subsection Accessing the Internal Modbus Slave Device. Appendix F in the User Manual lays out the register map. Here is a link to the User Manual.
Best Regards,
Colton Peltier