Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Reading TH110/CL110 realtime data using PAS600's internal wifi+webserver

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Reading TH110/CL110 realtime data using PAS600's internal wifi+webserver
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Lowell
Crewman Lowell Crewman
Crewman

Posted: ‎2025-10-17 07:44 AM

0 Likes
2
248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-17 07:44 AM

Reading TH110/CL110 realtime data using PAS600's internal wifi+webserver

Hi,

I have Th110 and CL110 installed in my ring main unit RM6. 

I intend to use PAS600 as data concentrator and connect my mobile phone via PAS600 internal wifi.

Will I be able to access its embedded web server thru my mobile phone to read real-time data, do configuration, and diagnostics? 

If it will work, do we have a procedure to set-up this and do I need more external device to make it work?

Thanks for the support

Kr

Lowell

 

Labels
  • Labels:
  • Product selection
Tags (6)
  • Tags:
  • CL110
  • english
  • PAS600
  • th110
  • webserver
  • wifi
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-10-19 09:56 PM

1 Like
0
222
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-19 09:56 PM

hello @Lowell 

When TH110/CL110 are paired to the PAS you will be able to get temperature readings + humidity inside the web pages. 

Are your TH/CL in your RMU provided with a zigbee dongle and working with Thermal App (former name) or Power Device on your smartphone ?

If yes you have to unpair the sensors from the APP and pair them to the PAS.

If you have a Zigbee gateway (ZBRN32, or PAS) just need to add the PAS in case of ZBRN32.

Kind Regards

See Answer In Context

Reply
Replies 2
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-10-19 09:56 PM

1 Like
0
223
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-19 09:56 PM

hello @Lowell 

When TH110/CL110 are paired to the PAS you will be able to get temperature readings + humidity inside the web pages. 

Are your TH/CL in your RMU provided with a zigbee dongle and working with Thermal App (former name) or Power Device on your smartphone ?

If yes you have to unpair the sensors from the APP and pair them to the PAS.

If you have a Zigbee gateway (ZBRN32, or PAS) just need to add the PAS in case of ZBRN32.

Kind Regards

Reply
Lowell
Crewman Lowell Crewman
Crewman

Posted: ‎2025-10-20 10:52 PM

0 Likes
0
205
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-20 10:52 PM

Thanks for advising that this is a viable solution; very helpful

Kr

Lowell 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore