Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Hi Xperts,
Just want to ask if the below cable can be used for RS485 cabling (PAS800L to meters).
Thanks,
Jedz
Link copied. Please paste this link to share this article on your social media post.
Hi Jedz @jedzruiz1985
Would suggest you to follow the instruction sheet specification.
And for further detailed wiring instruction, you can find from here https://www.se.com/in/en/faqs/FA221785/
Hope this helps!
Link copied. Please paste this link to share this article on your social media post.
hello,
Even this is not a belden certified modbus cable for RS485, It will depend on the length of the cable.
From what I see this is twisted pair, with overall shield/screen so should be OK.
For small distances LAN cables can be used.
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Thanks for the responses.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.