Protocol used between EGX300 or COMx to E.O. relay server for loading consumption data

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Re: Protocol used between EGX300 or COMx to E.O. relay server for loading consumption data
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Sabrina_Merelli
Lieutenant Sabrina_Merelli Lieutenant
Lieutenant

Posted: ‎2014-03-10 04:26 AM

0 Likes
10
1663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-10 04:26 AM

Protocol used between EGX300 or COMx to E.O. relay server for loading consumption data

A customer (ENEL) ask us details about the protocol used by EGX300 or COMx on the https channel for sending the energy data to the relay server. They want the protocol description so that they can evaluate delivering a compatible platform for acquire data from our field gateway (EGX300 or COMx)

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2014-03-13 06:33 AM

1 Like
0
1562
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-13 06:33 AM

Hi Sabrina,

I can only speak to the EGX300.  The EGX300 uses HTTP over SSLv3/TLSv1 (rfc 2818) without server certificate verification.

I hope this helps.

Randi

See Answer In Context

Reply
Replies 10
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2014-03-10 08:10 AM

0 Likes
1
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-10 08:10 AM

Hello Sabrina!

I'm not sure if I follow the question fully, but I'll give it a shot.

On either the EGX300, or Com'X 200, we can export/publish data to a HTTP (port 80) or HTTPs (port 443) server using the HTTP protocol.

Com'X 200

3228

EGX300

3229

After choosing this as your transport, the server will accept the data as a .CSV file.

Does this help?

James

Reply
Sabrina_Merelli
Lieutenant Sabrina_Merelli Lieutenant
Lieutenant

Posted: ‎2014-03-13 01:53 AM

0 Likes
0
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-13 01:53 AM

What the customer is asking is if it's available a description of the "exchange of packets" between the EGX/COMX and the relay sever. The sequence of requests/responses/acks between them.

Someone knows something about it?

Thank you

Sabrina

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2014-03-13 06:33 AM

1 Like
0
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-13 06:33 AM

Hi Sabrina,

I can only speak to the EGX300.  The EGX300 uses HTTP over SSLv3/TLSv1 (rfc 2818) without server certificate verification.

I hope this helps.

Randi

Reply
Anonymous user
Not applicable

Posted: ‎2014-03-13 07:43 AM

2 Likes
0
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-13 07:43 AM

The protocol itself is HTTP or HTTPS,

it is a standard, and normally you don't have to know the detail of the exchanged frames. You just have to start a HTTP / HTTPS server on your host

I would suggest to use "Apache" because it is an open source project, used by 80% of the servers)

Once the server is startet and configured, you will receive the CSV files from the Com'X 200 in the directory specified by HTTP server configuration.

The CSV file syntax is the same that the the one used by the EGX300 :

The difference is that the file is Ziped in order to reduce GPRS traffic

The first line is a comment that describes the header :

"Gateway Name,Gateway SN,Gateway IP Address,Gateway MAC Address,Device Name,Device Local ID,Device Type ID,Device Type Name,Logging Interval,Historical Intervals"

The second line is the header according to the previous format.

2 empty lines

The next line is a comment that describes the Topic ID list :

,,,Topic ID1,Topic ID2

The next line is the topics ID list according to the previous format.

2 empty lines

The next line is a comment that describes the variables time stamped value list :

Error,UTC Offset (minutes),Local Time Stamp,Active Energy (Wh),Reactive Energy (VArh)

The following lines are the variables value according to the previous format

Please find following the beginning of the file for a PM9c

//==============================================================================

Gateway Name,Gateway SN,Gateway IP Address,Gateway MAC Address,Device Name,Device Local ID,Device Type ID,Device Type Name,Logging Interval,Historical Intervals

DL_JEF,ComX2_srv_dev149,10.195.148.50,00:80:67:F9:31:90,PM9C_Id2,Resource-5,PM9C,PM9C,10,1085

,,,Topic ID1,Topic ID2

,,,1621,1625

Error,UTC Offset (minutes),Local Time Stamp,Active Energy (Wh),Reactive Energy (VArh)

0,120,09-04-2013 11:00:00,576322000,138687000

0,120,09-04-2013 11:10:00,576331000,138689000

0,120,09-04-2013 11:20:00,576340000,138691000

0,120,09-04-2013 11:30:00,576351000,138692000

0,120,09-04-2013 11:40:00,576363000,138695000

0,120,09-04-2013 11:50:00,576376000,138698000

0,120,09-04-2013 12:00:00,576389000,138701000

0,120,09-04-2013 12:10:00,576403000,138704000

0,120,09-04-2013 12:20:00,576417000,138707000

0,120,09-04-2013 12:30:00,576433000,138711000

0,120,09-04-2013 12:40:00,576447000,138714000

0,120,09-04-2013 12:50:00,576463000,138717000

0,120,09-04-2013 13:00:00,576478000,138720000

0,120,09-04-2013 13:10:00,576493000,138724000

0,120,09-04-2013 13:20:00,576506000,138727000

0,120,09-04-2013 13:30:00,576519000,138729000

0,120,09-04-2013 13:40:00,576527000,138732000

0,120,09-04-2013 13:50:00,576533000,138734000

Reply
Abdel
Lieutenant Abdel Lieutenant
Lieutenant

Posted: ‎2014-03-13 07:57 AM

0 Likes
4
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-13 07:57 AM

I believe the question was: wenn i have a webserver on the other side, it is normaly there to provide data over the http protocol and not to recieve data. For example when i am using the IIS, which configuration should i do to tell my webserver that it should recieve data ( the only way it webdav, i think)?

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2014-03-13 08:15 AM

2 Likes
3
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-13 08:15 AM

Hi Abdelatif,

So, in this case, there needs to be an application running on the server (IIS) that accepts the HTTP POST.  Using the screen capture above, the HTTP server will see "POST datafile1".  The server will associate this POST with an application that will get the data from the client and store it on the server.

Here's some information on Microsoft's site...

http://www.iis.net/configreference/system.webserver/handlers

Randi

Reply
Abdel
Lieutenant Abdel Lieutenant
Lieutenant

Posted: ‎2014-03-13 08:21 AM

0 Likes
2
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-13 08:21 AM

Thanks Randi,

did we have a sample Application for IIS, please.

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2014-03-13 10:09 AM

1 Like
1
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-13 10:09 AM

I have asked our test team for a sample.  I will send it when they deliver it to me.

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2014-03-14 08:29 AM

0 Likes
0
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-14 08:29 AM

I have sent the example via email.

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2014-03-14 08:29 AM

0 Likes
0
1563
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-03-14 08:29 AM

Would you update this thread as "answered", if you are satisfied with the reply?

Thank you.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore