Dear Community Members, We are currently experiencing a technical issue that is affecting the ability to create new posts. Our team is actively investigating the root cause and working to resolve it as quickly as possible. We apologize for the inconvenience and appreciate your patience. SE Community Team!
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
User | Count |
---|---|
111 | |
53 | |
46 | |
32 |
Link copied. Please paste this link to share this article on your social media post.
Hi,
I just wanted to mention that the Smartlink doesn't work with my setup under Monitoring - Real Time Data.
I rebooted the Com'X510 but that didn't help.
See two screenshots below:
This is the setup:
I added a custom pulse meter on channel 8 and an iEM2010 on channel 10.
It does work under Monitoring - Dashboards and Measurement Table.
See two screenshots below:
Publication via FTP does also work with the Smartlink.
Only I don't understand why I now do get .zip files.
I used an other Com'X510 some weeks ago and there .csv file were exported. (Also firmware version 2.1.17)
Used versions:
Best Regards,
Philippe
Posted: 2016-01-29 08:02 AM
Link copied. Please paste this link to share this article on your social media post.
About the Zip or CSV file format :
There is an option in the "Settings / General settings / Publication" page :
Compression Activated
Yes ==> ZIP
No ==> CSV
Regards
Jef