Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
81 | |
46 | |
28 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Hi
We state in Com´X datasheet 32 direct connected modbus slaves and additional 32 connected trough gateways.
How does this apply when the meters are PowerTags connected through PowerTag Link gateway ?
How meny Powertags can be connected to Com´X210/510 ?
BR/Anders
Link copied. Please paste this link to share this article on your social media post.
Hello @AndersDahlskog ,
As described in the Com'X User Manual, the Gateway cannot support more than 64 Modbus Slave devices. This applies also to the PowerTag sensors.
I have tested with a 66 PowerTag sensors connected to a PowerTag link HD. Then I added my PowerTag Link HD to my Com'X 510.
The Com'X discovered the 66 PowerTag sensors but I got the following message box :
So the limitation is 64.
Regards,
Romain
Link copied. Please paste this link to share this article on your social media post.
Hello @AndersDahlskog ,
As described in the Com'X User Manual, the Gateway cannot support more than 64 Modbus Slave devices. This applies also to the PowerTag sensors.
I have tested with a 66 PowerTag sensors connected to a PowerTag link HD. Then I added my PowerTag Link HD to my Com'X 510.
The Com'X discovered the 66 PowerTag sensors but I got the following message box :
So the limitation is 64.
Regards,
Romain
Link copied. Please paste this link to share this article on your social media post.
Hi Romain
Thank you for a clear answer, we have several project with this setup ongoing so it is vital for me to have this data when propose solutions to customers
BR/Anders
PAE EcoStuxure Power/Sweden
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.