Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Brand Logo
Help
  • Get started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
close
  • Community Home
  • Forums
    • By Topic
    • By Topic
      EcoStruxure Building
      • Field Devices Forum
      • SmartConnector Forum
      EcoStruxure Power & Grid
      • Gateways and Energy Servers
      • Metering & Power Quality
      • Protection & Control
      APC UPS, Critical Power, Cooling and Racks
      • APC UPS Data Center & Enterprise Solutions Forum
      • APC UPS for Home and Office Forum
      EcoStruxure IT
      • EcoStruxure IT forum
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • EcoStruxure Geo SCADA Expert Forum
      • Remote Operations Forum
      Industrial Automation
      • Alliance System Integrators Forum
      • AVEVA Plant SCADA Forum
      • CPG Expert Forum DACH
      • EcoStruxure Automation Expert / IEC 61499 Forum
      • Fabrika ve Makina Otomasyonu Çözümleri
      • Harmony Control Customization Forum
      • Industrial Edge Computing Forum
      • Industry Automation and Control Forum
      • Korea Industrial Automation Forum
      • Machine Automation Forum
      • Modicon PAC Forum
      • PLC Club Indonesia
      Schneider Electric Wiser
      • Schneider Electric Wiser Forum
      Power Distribution IEC
      • Eldistribution & Fastighetsautomation
      • Elektrik Tasarım Dağıtım ve Uygulama Çözümleri
      • Paneelbouw & Energie Distributie
      • Power Distribution and Digital
      • Solutions for Motor Management
      • Specifiers Club ZA Forum
      • Електропроектанти България
      Power Distribution NEMA
      • Power Monitoring and Energy Automation NAM
      Power Distribution Software
      • EcoStruxure Power Design Forum
      • LayoutFAST User Group Forum
      Energy & Sustainability Services
      • Green Building Scoring and Certification Forum
      Light and Room Control
      • SpaceLogic C-Bus Forum
      Solutions for your Business
      • Solutions for your Business Forum
      Support
      • Ask the Community
  • Knowledge Center
    • Building Automation Knowledge Base
    • Remote Operations Devices Knowledge Base
    • Geo SCADA Knowledge Base
    • Industrial Automation How-to videos
    • Digital E-books
    • Success Stories Corner
    • EcoStruxure IT Help Center
  • Events & Webinars
    • All Events
    • Innovation Talks
    • Innovation Summit
    • Let's Exchange Series
    • Partner Success
    • Process Automation Talks
    • Technology Partners
  • Ideas
    • EcoStruxure Building
      • EcoStruxure Building Advisor Ideas
      Remote Operations
      • EcoStruxure Geo SCADA Expert Ideas
      • Remote Operations Devices Ideas
      Industrial Automation
      • Modicon Ideas & new features
  • Blogs
    • By Topic
    • By Topic
      EcoStruxure Power & Grid
      • Backstage Access Resources
      EcoStruxure IT
      • EcoStruxure IT™ Advisor CFD
      Remote Operations
      • Remote Operations Blog
      Industrial Automation
      • Industrie du Futur France
      • Industry 4.0 Blog
      Power Distribution NEMA
      • NEMA Power Foundations Blog
      Energy & Sustainability Services
      • Active Energy Management Blog
      Light and Room Control
      • KNX Blog
      Knowledge Center
      • Digital E-books
      • Geo SCADA Knowledge Base
      • Industrial Automation How-to videos
      • Remote Operations Devices Knowledge Base
      • Success Stories Corner
  • companyImpact

Important Announcement: Community Back to Full Functionality

Dear Members, we are thrilled to announce that our Community is back to full functionality and that posts publication is now enabled again! We appreciate your patience during the last weeks. Learn more about our Community Guidelines. Thank you, Schneider Electric Community Team.

PowerLogic PowerTag Energy with delivered/reverse current on breaker-mounted types

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Communities
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PowerLogic PowerTag Energy with delivered/reverse current on breaker-mounted types
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Randi_Dolan
Commander Randi_Dolan Commander
45
Romain_Polette
Janeway Romain_Polette Janeway
41
JamesJeanette
Commander JamesJeanette Commander
28
Thierry_Baudard
Commander Thierry_Baudard Commander
23
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
snx
snx
Cadet

Posted: ‎2023-04-30 08:58 AM

0 Likes
4
508
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-30 08:58 AM

PowerLogic PowerTag Energy with delivered/reverse current on breaker-mounted types

Hello,

 

My task is to refurbish and extend an existing building control cabinet. Since space is rather limited, there is no space for full-sized energy-meters, so the powertag's would be my only option.

 

But i have one question that i could not find completly explained in the datasheets.


Can breaker-mounted powertags (A9MEM1521,1540,1522,1543,1541,1542) used in combination with a photovoltaic system that delivers energy to the grid?  This would mean that after the Breaker there is no consumer but an energy source delivering power to the grid, resulting in opposite current flow than for example a light bulb.

 

Can the devices be used for this application, or is it better to use a PowerTag Energy Flex 160A which seems to have switchable install direction, but cannot mounted on a breaker.

 

Thanks for your answers!

 

 

 

Labels
  • Labels:
  • Product selection
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Janeway Romain_Polette Janeway
Janeway

Posted: ‎2023-05-01 11:30 PM

0 Likes
1
481
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-01 11:30 PM

Hello @snx , 

 

Please check the Panel Server Modbus file:

https://www.se.com/ww/en/download/document/DOCA0241EN/

 

According to this file: PowerTag Energy Sensors 63A + Panel Server v001.005.001 seems compatible with Active Energy Delivered and Active Energy Received (total or per phase).

It means that Panel Server + PowerTag sensor 63A can be mounted on PV application.

 

@Szymon_Hochół can you confirm ? With older Panel Server FW, this feature was not available.

 

Thanks !

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Szymon_Hochół
Commander Szymon_Hochół Commander
Commander

Posted: ‎2023-05-02 06:54 AM

1 Like
0
469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-02 06:54 AM

Hi @snx ,

@Romain_Polette is correct - with current version of Panel Server and current version of PowerTag, you can see Active Energy Delivered and Active Energy Received as separate values:

Szymon_Hoch_0-1683035383707.png

 

Please note however that A9MEM15xx PowerTags are only 2-quandrant meters, as opposed to the rest of PowerTag family, which supports all 4 quadrants. Basically, you would get the delivered/received measurements for Active Energy only. This is why I would recommend to go with Flex 160A anyway, where you have bi-directional data for all kinds of energies:

Szymon_Hoch_1-1683035535973.png

 

Here is the summary for all types of PowerTags:

Szymon_Hoch_2-1683035649496.png

 

I hope this helps.

 

BR

 

See Answer In Context

Reply
Replies 4
Romain_Polette
Janeway Romain_Polette Janeway
Janeway

Posted: ‎2023-05-01 11:30 PM

0 Likes
1
482
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-01 11:30 PM

Hello @snx , 

 

Please check the Panel Server Modbus file:

https://www.se.com/ww/en/download/document/DOCA0241EN/

 

According to this file: PowerTag Energy Sensors 63A + Panel Server v001.005.001 seems compatible with Active Energy Delivered and Active Energy Received (total or per phase).

It means that Panel Server + PowerTag sensor 63A can be mounted on PV application.

 

@Szymon_Hochół can you confirm ? With older Panel Server FW, this feature was not available.

 

Thanks !

 

Romain POLETTE
Solution Architect - France Operations
Reply
Szymon_Hochół
Commander Szymon_Hochół Commander
Commander

Posted: ‎2023-05-02 06:54 AM

1 Like
0
470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-02 06:54 AM

Hi @snx ,

@Romain_Polette is correct - with current version of Panel Server and current version of PowerTag, you can see Active Energy Delivered and Active Energy Received as separate values:

Szymon_Hoch_0-1683035383707.png

 

Please note however that A9MEM15xx PowerTags are only 2-quandrant meters, as opposed to the rest of PowerTag family, which supports all 4 quadrants. Basically, you would get the delivered/received measurements for Active Energy only. This is why I would recommend to go with Flex 160A anyway, where you have bi-directional data for all kinds of energies:

Szymon_Hoch_1-1683035535973.png

 

Here is the summary for all types of PowerTags:

Szymon_Hoch_2-1683035649496.png

 

I hope this helps.

 

BR

 

Reply
snx
snx
Cadet

Posted: ‎2023-05-02 11:30 PM

0 Likes
0
454
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-02 11:30 PM

Szymon_Hochół  Romain_Polette

Thank you very much for the reply and clarification.

I have one additional question while looking at the screenshots. In the case of 100% delivery energy, will the current and power registers contain negative, positive or zero values?

For example, will 5A of delivery be displayed as "5A, -5A or 0A"?

Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-05-10 02:31 AM

2 Likes
0
411
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-05-10 02:31 AM

Hello,

The current will be always positive (RMS value).

The active power can be negative or positive:

  - if the active power is positive: the energy Delivered is incremented  (from the grid to the load)

  - if the active power is negative: the energy received is incremented (from the PV to the grid)

 

Obviously, you can use PowerTag Energy sensor 63Amps for your application.

 

BR

 

 

 

Thierry BAUDARD
Digital Power Technical Pre sale support International Zone
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

Additional options
You do not have permission to remove this product association.
 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this forum after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2023 Schneider Electric, Inc