Hi team,
I am working on an architecture that is using 19 devices (7 TCP/IP & 12 Serial). I'm planning on using two Panel servers, one for for each type of communication protocol.
Is it possible to have a PAS800 with the TCP/IP devices connected as well as having a PAS600 connected downstream with the serial devices connected?
If it is possible, will each device be logged individually on the PAS800?
Link copied. Please paste this link to share this article on your social media post.
Hello Dean,
If I understand well you want to use a Parent / Child gateway architecture: The Parent is the PaS800 and the Child is the PaS600.
On the PaS800 you will have the TCP/IP devices and yes you will be able too to discover and add at PaS800 level, each modbus devices from your PaS600.
Please find below a great video as an example about this kind of architecture: https://community.se.com/t5/Gateways-and-Energy-Servers/Panel-Server-video-Parent-and-child-gateway-...
Hope it help !
Link copied. Please paste this link to share this article on your social media post.
Hi @DeanZouganelis ,
Why not only using 1 single PAS800 on which you can connect as well the serial devices as also the TCP devices?