Link 150 + Controllogix Allen Brandley

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Link 150 + Controllogix Allen Brandley
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
96
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
41
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
camilo_gonzalez
Ensign camilo_gonzalez
Ensign

Posted: ‎2017-06-12 10:41 AM

0 Likes
10
1045
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-12 10:41 AM

Link 150 + Controllogix Allen Brandley

¿La comunicación del modulo "Link 150" y comunicación Ethernet de Allen Bradley en procesador ControlLogix es transparente?

Existe algún procedimiento paso paso que  tengan de dicha configuración, o tal vez descargar algún EDS, GSD ,EDD o algún bloque AOP  Schneider para su posterior programación en PLC Controllogix?

Gracias, saludos!

___________________________________________________________________________________

Is the communication of the "Link 150" module and Allen Bradley Ethernet communication in ControlLogix processor transparent?
Is there any step-by-step procedure you have for such configuration, or maybe download some EDS, GSD, EDD or some Schneider AOP block for later programming in PLC Controllogix?

Thanks

Regards

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
Tom_Stevenson
Picard Tom_Stevenson Picard
Picard

Posted: ‎2017-06-12 11:13 AM

2 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-12 11:13 AM

JUAN CAMILO ARIAS JARAMILLO​ Eduardo Fainblum​

Reply
Juan_Arias
Janeway Juan_Arias Janeway
Janeway

Posted: ‎2017-06-12 11:37 AM

1 Like
6
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-12 11:37 AM

Hola Camilo,

Que tipo de integracion piensas hacer con el PLC y el Gateway? Si el PLC ya tiene Ethernet para que necesitas el Gateway?

Vas a usar un algun software en especifico como maestro del PLC?

Saludos,

Juan

Reply
camilo_gonzalez
Ensign camilo_gonzalez
Ensign

Posted: ‎2017-06-15 09:37 AM

0 Likes
5
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-15 09:37 AM

Hola Juan, gracias por responder.

Lo que pasa es lo siguiente.

Tenemos 3 equipos PM3250 que queremos llevar a un sistema SCADA.

Por lo tanto, usamos la Link150 como Gateway de los 3 equipos PM3250 que están conectados por Modbus, y esta link la queremos visualizar en el PLC Controllogix.

No se si con eso te queda más claro a ver si me puedes ayudar.

De antemano, muchas gracias,

Saludos.

Reply
Juan_Arias
Janeway Juan_Arias Janeway
Janeway

Posted: ‎2017-06-15 10:54 AM

1 Like
4
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-15 10:54 AM

Hola Camilo,

Si tienes el gateway porque no accedes el medidor directamente desde el sistema SCADA? o mejor aun les vendes un PME

Si no, asegurate que el PLC pueda ser maestro Modbus TCP. Luego tienes que programar en el PLC el mapa modbus del medidor para importar los registros que requieras. No es necesario ningun tipo de archivo de configuracion.

Saludos,

Juan

Reply
camilo_gonzalez
Ensign camilo_gonzalez
Ensign

Posted: ‎2017-06-16 10:02 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-06-16 10:02 AM

Muchas gracias Juan.

Saludos.

Reply
camilo_gonzalez
Ensign camilo_gonzalez
Ensign

Posted: ‎2017-07-05 06:59 AM

0 Likes
2
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-05 06:59 AM

Estimado Juan:

Respecto de esto mismo, te comento que ya encontramos una solución para integrar los equipos PM3250 al sistema SCADA de la planta donde estamos trabajando. Para esto, utilizaremos una tarjeta Prosoft existente, para comunicar directamente en MODBUS RTU los equipos.

Mi nueva pregunta es la siguiente:

Yo pretendo incentivar a mi cliente para que instale el PME. Mi duda es si, puedo yo ir a buscar los datos directamente al PLC para poder monitorearlos desde el PME? En caso de que no pueda sacar los datos directamente desde el PLC, cuales serían los pasos a seguir?

Atento a tus comentarios, y de antemano muchas gracias!

Reply
Juan_Arias
Janeway Juan_Arias Janeway
Janeway

Posted: ‎2017-07-05 09:47 AM

0 Likes
1
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-05 09:47 AM

Hola Camilo,

Es posible leer los datos desde el PLC siempre y cuando este pueda actuar como esclavo Modbus TCP.

Leer los datos del PLC va a requerir mas ingenieria pues vas a tener que construir un driver personalizado para el PLC.

Mi recomendacion seria usar un Gateway Link150 para conectar los medidores aguas abajo y que PME y el PLC (si es necesario) sean maestros modbus TCP de los medidores. De esta forma puedes agregar los medidores nativamente a PME, y aprovechas los drivers existentes y sus beneficios en el software.

Saludos,

Juan

Reply
camilo_gonzalez
Ensign camilo_gonzalez
Ensign

Posted: ‎2017-07-05 10:56 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-05 10:56 AM

Estaba pensando en algo similar, pero ¿podría, utilizando comunicación MODBUS, dejar los equipos PM3250 como escalvos de 2 maestros diferentes (uno sería la Link150 y otro sería el PLC)?

Saludos,

Camilo

Reply
Juan_Arias
Janeway Juan_Arias Janeway
Janeway

Posted: ‎2017-07-05 11:08 AM

0 Likes
1
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-05 11:08 AM

No es posible si lo haces al puerto serial, solo un maestro por red serial.

Si lo haces a traves del gateway puedes tener multiples maestros Modbus TCP (en el lado ethernet) interrogando simultanemente el medidor.

Juan

Reply
camilo_gonzalez
Ensign camilo_gonzalez
Ensign

Posted: ‎2017-07-05 11:49 AM

0 Likes
0
985
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-07-05 11:49 AM

Aa claro, lo que pasa es que el Controllogix de Rockwell no conversa con la Link 150, por eso tuvimos que cambiar la forma de comunicar con el PLC . Y ahora que podemos comunicar los equipos con el PLC y visualizarlos en el SCADA, queremos también darles la posibilidad de instalar el PME.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of