ntegrate a third-party device which is a modbus temperature and vibration sensor to the pass800 through the Commissioning Web portal
Kind regards,
I am creating a template for the PASS800L for a temperature and vibration sensor for a motor, but when creating the modbus registers in the template there is no default library that allows adding the values from the sensor register table. If I add them without using any of the library recommendations it allows me to create the template, but when importing it into the PASS800L it tells me "INVALID MODEL".
Please can you help me with information or some kind of template that I can use as an example to create the template mentioned.
I appreciate the support and attention.
Link copied. Please paste this link to share this article on your social media post.
hello @krisconde10,
I do not see your custom model associated to a device if it is QM30VT2 ?
Regarding your custom model I see a Float32 measurement which is having a custom measurement name.
From what I see you are having measurement in your custom model, do you have frames ?
Can you add your custom model ?
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
hello @krisconde10,
There is unit symbolic name with too long value (> 16 Characters)
For "RMS Velocity mmsec" measurement, change "RMS Velocity mmsec" Unit (18 characters) to a shorter unit name and it will work.
Regards
Link copied. Please paste this link to share this article on your social media post.
@Eric_HAVAS have you reported this to EPC W team ? info bubble is mentioning it but we should not be able to enter more than 16 characters or have a warning....
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Hello dear, @Guillaume_Evrard
I would like to tell you that the Device is the QM3VT2 Sensor, for which we are creating the modbus template, for the Pass800L, the values that we have in the modbus register map are in the FLOAT32 format, and the measurement is customized, they are not found in the default libraries of the Commissioning Web portal, and in fact I want to integrate it
Link copied. Please paste this link to share this article on your social media post.
Hi dear @Eric_HAVAS,
I will try to make the suggested change and give you feedback,
Thanks for the support!