Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Integrate a third-party device which is a modbus temperature and vibration sensor to the pass800 through the Commissioning Web portal

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Integrate a third-party device which is a modbus temperature and vibration sensor to the pass800 through the Commissioning We...
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
99
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
44
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All
Related Products
product field
Schneider Electric
EcoStruxure Panel Server

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
krisconde10
krisconde10 Cadet | EcoXpert Master
Cadet | EcoXpert Master

Posted: ‎2024-10-09 04:35 PM

0 Likes
6
921
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-09 04:35 PM

Integrate a third-party device which is a modbus temperature and vibration sensor to the pass800 through the Commissioning Web portal

ntegrate a third-party device which is a modbus temperature and vibration sensor to the pass800 through the Commissioning Web portal

 

Kind regards,

 

I am creating a template for the PASS800L for a temperature and vibration sensor for a motor, but when creating the modbus registers in the template there is no default library that allows adding the values from the sensor register table. If I add them without using any of the library recommendations it allows me to create the template, but when importing it into the PASS800L it tells me "INVALID MODEL".

Please can you help me with information or some kind of template that I can use as an example to create the template mentioned.

I appreciate the support and attention.

  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Attachments
Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 6
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-10-09 09:48 PM

0 Likes
1
891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-09 09:48 PM

hello @krisconde10,

I do not see your custom model associated to a device if it is QM30VT2 ?

Regarding your custom model I see a Float32 measurement which is having a custom measurement name.

 

From what I see you are having measurement in your custom model, do you have frames ?

Can you add your custom model ?

Kind Regards

 

 

Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2024-10-10 01:42 AM . Last Modified: ‎2024-10-10 01:46 AM

1 Like
1
871
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-10 01:42 AM

hello @krisconde10,
There is unit symbolic name with too long value (> 16 Characters)
For  "RMS Velocity mmsec" measurement, change  "RMS Velocity mmsec" Unit (18 characters) to a shorter unit name and it will work.
Regards

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-10-10 10:09 PM

0 Likes
1
854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-10 10:09 PM

@Eric_HAVAS have you reported this to EPC W team ? info bubble is mentioning it but we should not be able to enter more than 16 characters or have a warning....

 

 

Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2024-10-10 11:16 PM

1 Like
0
848
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-10 11:16 PM

@Guillaume_Evrard: Of course

Reply
krisconde10
krisconde10 Cadet | EcoXpert Master
Cadet | EcoXpert Master

Posted: ‎2024-10-11 08:31 AM

0 Likes
0
822
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-11 08:31 AM

Hello dear, @Guillaume_Evrard 

I would like to tell you that the Device is the QM3VT2 Sensor, for which we are creating the modbus template, for the Pass800L, the values ​​that we have in the modbus register map are in the FLOAT32 format, and the measurement is customized, they are not found in the default libraries of the Commissioning Web portal, and in fact I want to integrate it

Reply
krisconde10
krisconde10 Cadet | EcoXpert Master
Cadet | EcoXpert Master

Posted: ‎2024-10-11 08:34 AM

0 Likes
0
821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-10-11 08:34 AM

Hi dear @Eric_HAVAS,

I will try to make the suggested change and give you feedback,

Thanks for the support!

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of