How to... Com'X200 Factory Reset
In certain instances, you might want to factory reset your Com'X200. For example, there was a small bug in the firmware prior to 1.0.8 that was creating erratic behavior. So in order to factory reset, it's easy:
1) Stop the power of your Com'X200.
2) Press the two buttons on the front panel together (keep it pressed)
3) Power the box
4) Wait for 15seconds or until you see the power led blink 3 times in orange
5) Stop pressing the two buttons
6) Wait for the box to come back (takes about 5 minutes)