Gas metering in EGX 300 visible ? DI on PM750

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Gas metering in EGX 300 visible ? DI on PM750
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
98
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
43
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
josgrafe
Lieutenant JG josgrafe
Lieutenant JG

Posted: ‎2013-10-04 02:35 AM

1 Like
11
1287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-04 02:35 AM

Gas metering in EGX 300 visible ? DI on PM750


We have a gas puls connected on the PM750 digital input.

In ION6 we can work with this signal. (countervalue)

Is it also possible to see this input and a trend in the EGX 300?

Looking forward to your suggestions.

regards Jos Gräfe

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2013-10-04 06:26 AM

2 Likes
4
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-04 06:26 AM

Hello Jos,

There are a couple of solutions, that are not really ideal, but will work.

You can display the status and the count of the input in the real time and logging features using the Custom Device Type Generator.  With this tool, you can create a device type that can display any values that the PM750 makes available via Modbus.  You can also scale these values to make the counts more meaningful.  For example, you can multiply the number of counts on the input by a number representing something like the number of cubic meters per hour each pulse represents.  However, with this solution, you will not be able to use the Trending feature on-board the EGX300.

It is possible, however, to create a custom page to do pretty much whatever you would like.  You could create a "Trending" web page for the PM750 that reads the value of the input on a periodic basis (once every couple of seconds or so) and then display the results on a graph.  There are several graphing tools available for free on the internet that you could upload to one of the custom web page directories.  Also, the EGX300 makes the device list available to applications via the "devlist.xml" file.  You could use the contents of this file to determine the Modbus addressing information for the PM750s defined in the system.

If you would like any additional information about the Custom Device Type Generator or Creating Custom Web Pages in the EGX300, please let me or James Jeanette know.  We will forward the appropriate documents describing these features to you.

Please let me know if I can be of further assistance in any way.

Randi

See Answer In Context

Reply
Replies 11
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2013-10-04 06:26 AM

2 Likes
4
1166
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-04 06:26 AM

Hello Jos,

There are a couple of solutions, that are not really ideal, but will work.

You can display the status and the count of the input in the real time and logging features using the Custom Device Type Generator.  With this tool, you can create a device type that can display any values that the PM750 makes available via Modbus.  You can also scale these values to make the counts more meaningful.  For example, you can multiply the number of counts on the input by a number representing something like the number of cubic meters per hour each pulse represents.  However, with this solution, you will not be able to use the Trending feature on-board the EGX300.

It is possible, however, to create a custom page to do pretty much whatever you would like.  You could create a "Trending" web page for the PM750 that reads the value of the input on a periodic basis (once every couple of seconds or so) and then display the results on a graph.  There are several graphing tools available for free on the internet that you could upload to one of the custom web page directories.  Also, the EGX300 makes the device list available to applications via the "devlist.xml" file.  You could use the contents of this file to determine the Modbus addressing information for the PM750s defined in the system.

If you would like any additional information about the Custom Device Type Generator or Creating Custom Web Pages in the EGX300, please let me or James Jeanette know.  We will forward the appropriate documents describing these features to you.

Please let me know if I can be of further assistance in any way.

Randi

Reply
LaurentCoene
Captain LaurentCoene Captain
Captain

Posted: ‎2013-10-04 09:39 AM

1 Like
1
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-04 09:39 AM

I actually wrote an article on how to do that with a PM3255 a long time ago. It's exactly as Randi is describing.

Here are some of the details:

http://energyoperation.info/2012/08/28/send-wages-pulse-data-through-a-pm3255-and-an-egx300-to-the-c...

Reply
josgrafe
Lieutenant JG josgrafe
Lieutenant JG

Posted: ‎2013-10-06 10:57 PM

0 Likes
3
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-06 10:57 PM

Thanks guys,

I will experiment with these options.

Maybe It will be a good add-on for the EGX300 software is there is a way to see WAGES information graphically.

(Is this covered in the Com X 200? )

Jos.

Reply
josgrafe
Lieutenant JG josgrafe
Lieutenant JG

Posted: ‎2013-10-07 01:27 AM

0 Likes
1
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-07 01:27 AM


Randi,

please send me the documents that you described. ( j.graefe@beenen.nl)

Regards Jos

Reply
LaurentCoene
Captain LaurentCoene Captain
Captain

Posted: ‎2013-10-07 01:35 AM

2 Likes
2
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-07 01:35 AM

You can do the same type of Custom Device Type in the Com'X200, however, there's one major difference: the Com'X200 cannot do any sort of reporting (can't be used as an on-site solution). You can only do the data-logging and push the data to the cloud (REM, Energy Operation or other third party) so it might not work for what you intend to do. The Com'X500 (expected in 2014) will be the replacement of the EGX300 and will do all the Com'X200 is awesome at, and will allow local reporting.

Reply
josgrafe
Lieutenant JG josgrafe
Lieutenant JG

Posted: ‎2013-10-07 01:41 AM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-07 01:41 AM

Thank you for the information. I will offer the EGX300 for now with an eWON 2101 CD UMTS  to connect to it. ( VPN - webbased)  , Will VPN be available in the Com'X500 ?

Reply
sesa205726_brid
Lieutenant JG sesa205726_brid Lieutenant JG
Lieutenant JG

Posted: ‎2013-10-07 05:01 AM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2013-10-07 05:01 AM

Hi Randi,

with the second option you can display the trend but you can't do the logging of the variables.

It would better involve the digital inputs, in the logging file, for each device having digital inputs. In Italy this are asked very frequently.

The customers solve this problem creating a new device with all electrical variables and adding digital inputs, losing the trends.

Thank you Randi

By

Reply
sesa341891
sesa341891 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-10-21 04:42 PM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-21 04:42 PM

Estimate Randi

Could you please send me some information about how to create Custom Web Pages in the EGX300?

Thanks in advance!

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2014-10-22 10:54 AM

2 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-22 10:54 AM

Thanks Laurent.  One correction...Com'X 510 will be available in Q1 2015.  There is an ongoing project which will enable VPN through the Com'X product line.  More to come on that later.

James

Reply
Anonymous user
Not applicable

Posted: ‎2014-10-22 06:33 PM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-22 06:33 PM

The article is no longer there. Any idea what is the new link?

Reply
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2014-10-23 02:56 PM

0 Likes
0
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-10-23 02:56 PM


Hi Jos.  Here is a direct link to the Custom Device Type Generator document in SEC:

https://powersolutionscommunity.schneider-electric.com/docs/DOC-1063

Let us know if you have any questions.

Thanks!

James

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of