Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82502members
350090posts

Firmware EGX300 v4.370

Gateways and Energy Servers

Get expert answers to your questions regarding Schneider Electric Gateways & Energy Servers, from product selection to implementation and troubleshooting. Collaborate with a global community of experts and peers, get support and share your experiences by subscribing to the Schneider Electric Community Gateways and Energy Servers forum today.

JamesJeanette
Commander Commander
Commander

Firmware EGX300 v4.370

RELEASE NOTES:

Updates:

Version 4.370 firmware provides:

  • Added Time-out for SMTP and HTTP Data Log Export
  • Updated ModbusTCP Client to handle connections closed by ModbusTCP Servers
  • Modified Data Log Export algorithm
  • Added Acti9 Dashboard functionality

   

Device Support:

  • Added the following devices
    • Vigilohm IM400
    • iEM3350
    • iEM3355
  • Added Input Metering Pulse Count to iEM3x55 and PM3255 Logging
  • Added Trending Support for the Conext TL
  • Updated ION7650 Reset Handling
  • Changed Micrologic E Min/Max Reset to reset both Min and Max values
  • Changed PM5350 "Total Energy" from "Energy Delivered + Received" to "Energy Delivered-Received"
  • Fixed issue with logging strings not matching topic for PM5100/PM5300, EM4800, PM5350xB, PM5350, and PM5500
  • Fixed issue with iEM3155 and iEM3255 not displaying Input 1 Pulse Weight correctly
  • Added check to PM3250 device type to determine whether or not to display Input Metering Values
  • Fixed Per Phase Power Trending in the iEM3150

Additional Product/Support Improvements




Attachments
9 Replies 9
sesa205726_brid
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
74

Re: Firmware EGX300 v4.370

Hi , in the list of features of last firmware version of the EGX300 is not clear if EGX300 supports reading the PM5300 through TCP/IP connection.

Thanks

BR

avintola
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
74

Re: Firmware EGX300 v4.370

James Jeanette

Hi, James! I have a quick question about firmware updates. When updating the firmware of EGX300, how will it affect the logged data in the unit and the current configuration. Will the logged data be erased and the configuration reverted to the default setup?

All the best,

Alyssa

JamesJeanette
Commander Commander
Commander

Re: Firmware EGX300 v4.370

Hello Alyssa.

The logged data and configuration will remain; however, we do have some recommendations depending on which version you are updating from.

If you currently are running Firmware Version 3.7, follow this for 4.370:

4928

If you currently are running Firmware Version 3.8 (or GREATER), follow this for 4.370:

4929

*As a reminder.  You need both the Firmware file, and the Disk Update file to perform an EGX300 upgrade.  You apply the Disk Update file in the same manner (FTP) as the Firmware file, but only AFTER the Firmware file is transferred, and the EGX300 reboots.

I hope this helps.

James

FYI:

avintola
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
74

Re: Firmware EGX300 v4.370

Thanks, James!

Jun_Escano
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
74

Re: Firmware EGX300 v4.370

Same here testing with the PM5320 but somehow it is not working (Via ION Setup i can get connection)

Jun_Escano
Lieutenant JG Lieutenant JG
Lieutenant JG
0 Likes
0
74

Re: Firmware EGX300 v4.370

Never mind i just forgot that the new firmware will fix this November 2014

JamesJeanette
Commander Commander
Commander
0 Likes
0
74

Re: Firmware EGX300 v4.370

This is correct.  The new version of EGX300 firmware will allow for remote ID connection to 255.

James

maxencevanhove
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
74

Re: Firmware EGX300 v4.370

James, Hi!

Regarding the fix "Issue with logging strings not matching topic for PM5100/PM5300, EM4800, PM5350xB, PM5350, and PM5500", I'd like to understand if Active Energy was recorded under a wrong topic?


We currently have the following topics available under a PM5100:

5042

Would updating the firmware add Active Energy kWh to that list?

Thanks in anticipation!

-Maxence

arjanbijker
Schneider Alumni (Retired)
Schneider Alumni (Retired)
0 Likes
0
74

Re: Firmware EGX300 v4.370

HI James,

it seems that like logging of pulse count on the PM3255 is not working correctly.

Please see attached screenshots

50895090