Hallo, I am configuring a G3200 to integrate 3rd party modbus products. It is a Kries IKI-50 condition monitor. But I found writing the i61850 configuration file (cid) is getting more and more complicated. The G3200 already found the Modbus device (webserver/diagnostics view), but connecting via MMS with a i61850 client, i still have problem mapping the registers to i61850 nodes and quality/timestamp are indicating, it is not properly what i did. Are there predefined files for 3rd party products available? In the manual, an email address PowerLogic.G3200@schneider-electric.com should provide them, but it is no longer available.
Any ideas? Or is this a legacy product - is there a successor?
Link copied. Please paste this link to share this article on your social media post.
I believe Ravindra Gadagoju/IN/Schneider is the contact person for this device. They should be able to help you.
Link copied. Please paste this link to share this article on your social media post.
Yes, This is correct.
I wish you good luck for your integration, as for this device there is nearly no support at all (I had the situation myself this year, that I had to modify the driver for the PM8xx, but it was very hard, even nearly impossible to get support on this)!
Cheers
Daniel
Link copied. Please paste this link to share this article on your social media post.
For now, you have to start with the SEPAM CET850 Tool to create an empty cid-file, but then you have to add your devices and Modbus registers manually as described in the manual.
Important is to have the correct MD2-Hash in the file. This check is performed by the G3200 before upload.
@Randi Thanks for your contact, he helped me out on a few issues though occupied with other project activities.
My file is working so far, still needs some minor corrections, but I could load it into the SAS (Pacis from SE) and get some values from the Kries devices. I'll post the file later on.