Ethernet Gateway (Link150/ EGX150) HTTPS?

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Ethernet Gateway (Link150/ EGX150) HTTPS?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Darren_Pearce
Lieutenant | EcoXpert Master Darren_Pearce Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2019-11-13 05:27 AM

1 Like
14
4792
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2019-11-13 05:27 AM

Ethernet Gateway (Link150/ EGX150) HTTPS?

Hi All,

 

I had a coversation during a site visit yesterday, where the customer was telling me the Link150/EGX150 was due a firmware update, to enable the web interface to be HTTPS.

 

Can anyone confirm if this is a current task in the roadmap for the current hardware.

 

Or

 

If a new hardware version of the Link150/EGX150 would have to be launched to enable the protocol?

 

We have many of these devices on sites and often have the question raised if all the hardware supports HTTPS.

 

Regards

 

Darren

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2020-05-21 11:58 AM

0 Likes
0
4688
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-21 11:58 AM

When HTTPS is enabled, EGX150 will stop communicating over HTTP and port 80 will not be used.

See Answer In Context

Reply
Replies 14
Anonymous user
Not applicable

Posted: ‎2020-01-08 10:05 AM

0 Likes
1
4779
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-08 10:05 AM

Hi the community members can you help this member on this topic please?

 

@Romain_Polette   do you think you can advise on this topic?

 

@Darren_Pearce  , in the meantime, please check the Knowledge base, maybe you can find useful information.

 

But if you still in the same situation please do not hesitate to inform us here.

 

Have a nice day.

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2020-01-08 12:29 PM

0 Likes
1
4776
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-08 12:29 PM

Hi

 

The Link 150/EGX150 team does not monitor this board.  The best way to obtain this information would be to go through the Customer Care Center and have them contact the product team.

 

Regards,

Randi

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2020-01-08 10:14 PM . Last Modified: ‎2022-10-19 02:35 AM

0 Likes
0
4772
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-08 10:14 PM

Hello @FirdousKhan , 

 

Dedicated thread here : https://community.se.com/t5/Gateways-and-Energy-Servers/Link-150-New-Firmware-Release-Available-v-5-...

 

Darren is closely following the topic.

Thanks.

Romain POLETTE
Solution Architect - France Operations
Reply
Darren_Pearce
Lieutenant | EcoXpert Master Darren_Pearce Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-01-09 04:39 AM

1 Like
0
4768
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-09 04:39 AM

Hi,

 

I new firmware was released for the Link150 which includes HTTPS however the function of disabling the HTTP access does not exist, leaving a vulnarability.

 

Regards

 

Darren

Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2020-01-09 06:45 AM

1 Like
9
4762
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-09 06:45 AM

From the Link150 Team:

 

An official firmware had been released on 3rd week of December 2019 which has default enabled by HTTPS
For existing customer then can upgrade the firmware and it is available in se.com with FW 005.001.015

Regards,

Randi

Reply
Darren_Pearce
Lieutenant | EcoXpert Master Darren_Pearce Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-01-13 05:24 AM

0 Likes
8
4756
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-01-13 05:24 AM

Randi,

 

Yes the new firmware was released for the Link150 which includes HTTPS however the function of disabling the HTTP access does not exist, leaving a vulnarability.

 

Does the Link150 Team have a response to that?

 

Regards

 

Darren

Reply
Anonymous user
Not applicable

Posted: ‎2020-04-02 08:46 AM

0 Likes
7
4732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-02 08:46 AM

Hi Darren,

I am Asif, product prime in Global Technical Support for Gateways and Com'X. Here is the answer to your question:

When HTTPS mode is activated, all data transacted over HTTP protocol is redirected to HTTPS automatically. In this state, all packets are forwarded to HTTPS port instead of HTTP port.

 

Regards,

Asif

Reply
Darren_Pearce
Lieutenant | EcoXpert Master Darren_Pearce Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-04-17 04:14 AM

0 Likes
6
4723
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-17 04:14 AM

Hi Asif,

 

Thank you for your response and the details you have provided, one question to your information, if the data request is forwarded from the HTTP to the HTTPS port for the request, how is the response correctly returned if it is providing an encripted resonse to a none encripted request?

Is it possible to shutdown port 80 rather than forward this on?

 

As you may be the most appropriate person for this product, can i also ask a question that has bugged me for quite a time with the Link150/EGX150, the device has a RTC i assume, with the menu option to adjust it, why is this not either intergrated to the PME time broadcast to self set, or include NTP settings perhaps?

 

Regards

 

Darren

Reply
Anonymous user
Not applicable

Posted: ‎2020-04-23 12:47 PM . Last Modified: ‎2020-04-23 12:48 PM

0 Likes
5
4715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-23 12:47 PM

Hi Darren,

 

Thanks for your questions.

 

If HTTPS is enabled in EGX150, the certificate must be trusted at the customer end. If the customer lacks a certificate from a trusted authority or use HTTP instead of HTTPS, the HTTPS connection must not be enabled inside the EGX150. Cause, this kind of non-ideal communication (EGX150 having HTTPS and the customer using HTTP), leaves Man-in-the-middle type vulnerability in the system.

 

To answer the second part of your question, EGX150 implements neither RTC nor SNTP currently (reference: page 43 of the attached EGX150 User Guide).


One has to set the date and time manually from EGX150's web page as mentioned on the same page.

 

Regards,
Asif

Attachments
Reply
Darren_Pearce
Lieutenant | EcoXpert Master Darren_Pearce Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-04-24 02:08 AM

0 Likes
4
4711
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-04-24 02:08 AM

Hi Asif,

 

Thanks for your response, however your reply raises more concerns than my initial thoughts.

 

The site this query is based on does have security certificates for the domain, the site has gone through rigorous PEN testing for security too.

While i understand that if we enabled HTTPS access, we would use HTTPS in the browser to connect to the device ourselves, for any setting changes, it does sound by still leaving HTTP enabled and forwarding on the request internally to HTTPS, if a malicious party did carryout actions to create a man-in-the-middle attack, the gateway would be vulnarable to this action?

 

I also did believe the clock would have been maintained under power outages by an onboard backup supply, as i see little point in an ability to set the time and date if this is not maintained at all internally, an SNTP ability would resolve this issue.

 

Regards

Darren

Reply
Anonymous user
Not applicable

Posted: ‎2020-05-07 02:54 PM

0 Likes
3
4700
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-07 02:54 PM

Hi @Darren_Pearce 

 

Apology for the late reply.

 

Can you kindly explain a little more the following section from your last response:

While i understand that if we enabled HTTPS access, we would use HTTPS in the browser to connect to the device ourselves, for any setting changes, it does sound by still leaving HTTP enabled and forwarding on the request internally to HTTPS, if a malicious party did carryout actions to create a man-in-the-middle attack, the gateway would be vulnarable to this action?

On SNTP and RTC, I agree with you. Unfortunately, as of now, the EGX150 has neither of the time-keeping technology implemented.

Regards,

Asif

Reply
Darren_Pearce
Lieutenant | EcoXpert Master Darren_Pearce Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2020-05-13 03:21 AM

0 Likes
2
4697
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-13 03:21 AM

Hi Asif,

 

From your original post;

 

'If the customer lacks a certificate from a trusted authority or use HTTP instead of HTTPS, the HTTPS connection must not be enabled inside the EGX150. Cause, this kind of non-ideal communication (EGX150 having HTTPS and the customer using HTTP), leaves Man-in-the-middle type vulnerability in the system.'

 

I have highlighted a selection of 'what if occurances'.

My customer when we set the system up wants to secure the system as much as possible, the EGX150 has the ability to use HTTPS, so i enable that function. But i can't disable HTTP.

 

It appears that because i can't disable HTTP there is a Man-in-the-middle type vulnerability?

 

If i could disable HTTP (Port 80) in the configuration, so the EGX150 does not forward a request internally, would that stop the vulnerability?

 

Regards

 

Darren

Reply
AndersDahlskog
Lieutenant AndersDahlskog Lieutenant
Lieutenant

Posted: ‎2020-05-18 06:20 AM

0 Likes
0
4692
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-18 06:20 AM

Hi we get reports that with it is no longer possible to double click on the icon in Network explorer to open webbpage with the latest firmware. Instead you have to right click and then proporties to to click on the webbpage link there. Have observed the same with PM8000.

Has this anything to do with the above question/answer ?

 

BR/Anders

Reply
Anonymous user
Not applicable

Posted: ‎2020-05-21 11:58 AM

0 Likes
0
4689
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-05-21 11:58 AM

When HTTPS is enabled, EGX150 will stop communicating over HTTP and port 80 will not be used.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore