EGX300 as a converter
Gateways and Energy Servers
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • EGX300 as a converter
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
58
Randi_Dolan
46
sesa300708
sesa300708 Schneider Alumni (Retired)
Posted: ‎2016-03-02 09:42 PM
2435
Good day,
Our customer has an EGX300. They have PME 7.2.2.
They will install ION8650 power meter and hook it to PME. The distance of the power meter to the network switch is 350 meters.
RS485 will be used since lan cable is only for 100 meters. The protocol is ION since the ION8650's data is limited to Modbus RTU protocol
My question is, can the EGX300 be used as a converter only?
I know EGX300 doesn't support ION protocol.
Thank you,
Josef
Yu_Diao
Commander Yu_Diao Commander
Commander
Posted: ‎2016-03-02 11:22 PM
The short answer is no. If EGX300 is used, ION8650 will only be reached through ModRTU.
Sent from my mobile device.
Replies 8
Yu_Diao
Commander
sesa22585
sesa22585 Schneider Alumni (Retired)
Posted: ‎2016-03-03 07:08 AM
5
2253
The Link150 (Commercial Reference EGX150) is new on the market and has an update coming in April that can pass through the ION protocol from Serial to Ethernet.  Talk to your Schneider Country representative to see if it is launched in your area.
sesa300708
Posted: ‎2016-03-03 05:22 PM
Thank you so much, Yu and Bobbie!
sesa360183_brid
sesa360183_brid Schneider Alumni (Retired)
Posted: ‎2016-03-16 09:16 PM
4
2253
This is from the specification document. So I assume that the "Powerlogic" here confirms the converter capability, am I right? Thanks!
Adrian_Dicea
Janeway Adrian_Dicea Janeway
Janeway
Posted: ‎2016-03-17 12:14 AM
2253
PowerLogic (SY/MAX) != ION
sesa360183_brid
Posted: ‎2016-03-22 09:08 AM
2253
So I guess, this needs some clarification fromBobbie Meredith? Thanks!
sesa22585
Posted: ‎2016-03-22 09:29 AM
1
2253
Link150 can support Modbus and Powerlogic (Symax) in the same daisy chain.
In the next firmware version you can put the Link150 in ION pass through mode and it can pass through ION from serial to Ethernet.  This mode does NOT support Modbus or Powerlogic. You must have either a Modbus/Powerlogic or ION daisy chain.
sesa360183_brid
Posted: ‎2016-03-28 11:05 PM
Thank you very much, Bobbie. This clears it up.