EGX 300, more instrument with the same Modbus address
Gateways and Energy Servers
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • EGX 300, more instrument with the same Modbus address
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
59
Randi_Dolan
46
sesa78383_bridg
Crewman sesa78383_bridg Crewman
Crewman
Posted: ‎2015-08-25 07:18 AM
932
Dear collegues,
I'm using a PLC as a gateway and concentrator for 10 third party power meters communicating in profibus. I configured on the PLC different memory register areas for different instruments ( e.g from MW 100 to MW 200 for instrument 1, from 201 to 300 for instrument 2 and so on). I want to read the PLC memory areas containing the power meters data with a EGX300,  In order to have local buffer ( a PME with ETL is required). I'm configuring 10 different custom device type , so I can have one csv for each instrument. The problem is that the EGX300 dos not accept the configuration of more instruments with the same modbus address( see picture below), that is the modbus address of the PLC of course.
Does someone knows if it is possible to make the EGX 300 accept this configuration. I'd appreciate any other  ideas for the given system.
Thanks alot
Tags (2)
  • modbus
  • pme
Posted: ‎2015-08-31 10:55 PM
I do not know any solution using the EGX300, but you may replace it by an Com'X 200.
In this new familly of gateway there is no restriction on the modbus slaves.
Regards