Connecting Modbus SL power meters to PAS800

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Connecting Modbus SL power meters to PAS800
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
109
Guillaume_Evrard
Captain Guillaume_Evrard Captain
52
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All
Related Products
product field
Schneider Electric
EcoStruxure Panel Server Advanced

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
lasalm1989
Crewman lasalm1989
Crewman

Posted: ‎2025-09-05 10:15 AM

0 Likes
3
60
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-05 10:15 AM

Connecting Modbus SL power meters to PAS800

Hi,

I have a requirement to increase the number of Modbus SL power meters to PAS800. Since PAS800 only support 32 Modbus SL devices, I'm planning to connect the power meters to PAS800 using PAS600 . I can't increase to network ports available in the upstream network.

Please recommend my design is correct or not, please recommend any other options available.


Please find system specifications below
Power meter : METSEPM2220
Polling interval : 15mins

Baud rate : 19200

Upstream network bandwidth : 300Mbbs

 

Please recommend how many PAS600 can be connected to 1 PAS800

 

  • Thumbnail of EcoStruxure Panel Server Advanced
    Schneider Electric
    EcoStruxure Panel Server Advanced
View products (1)
Labels
  • Labels:
  • Product selection
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-09-08 09:27 PM

0 Likes
2
50
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-08 09:27 PM

hello @lasalm1989 ,

What do you want to do with your PAS800, only modbus tcp gateway ?

PAS can accept only 128 modbus tcp devices, devices connected to PAS600 (Child gateway) will be modbus tcp devices. You will have to play with the virtual IDs if you want to match the IDs.

Kind Regards 

Reply
lasalm1989
Crewman lasalm1989
Crewman

Posted: ‎2025-09-11 12:20 AM

0 Likes
1
31
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-11 12:20 AM

Hello Guillaume,

Thank you for your explanation. I would like to humbly clarify my requirement:

  • The PAS600 is intended to connect additional Modbus SL power meters (METSEPM2220) to the PAS800, helping to overcome the 32-device limit while also reducing the number of Ethernet ports needed on the upstream switch.

  • The PAS800 is mainly used to log the data locally, so that in the event of an upstream network failure, no measurement data is lost.

  • Since the number of upstream switch ports is limited, my main concern is understanding how many METSEPM2220 meters can be practically connected to one PAS800 through PAS600 units, given the polling interval (15 minutes), baud rate (19200), and upstream bandwidth (300 Mbps).

I would be grateful if you could kindly confirm whether this design is appropriate and advise on the recommended number of PAS600 units that can be connected to one PAS800.

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-09-11 08:57 PM

1 Like
0
25
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-09-11 08:57 PM

hello,

128 +32, regarding data sampling you need to see if you are below the PAS800 limit, for modbus serial link you need to make the computation taking into account baudrate, number and type of registers, number and time of devices and time it takes to return the modbus com. Pay attention that PAS800 will check communication with the device every 15s by polling it and in case of 15 min sampling, PAS will poll all the registers every minute.

Kind Regards

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore