Ask our Experts
Didn't find what you are looking for? Ask our experts!
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Search in
User | Count |
---|---|
115 | |
56 | |
46 | |
32 |
Posted: 2017-07-19 06:13 AM
Link copied. Please paste this link to share this article on your social media post.
Hi all,
I want a configure 2 port Ethernet of Link 150 same image below.
It mean, I have two LINK 150 and one PC.
I will connect (Cable Ethernet) from port Eth1 of LINK 150_A to port Eth2 of LINK 150_B
After, I will connect (Cable Ethernet) from port Eth1 of LINK 150_B to port Ethernet of PC.
Can i do it? Yes or No and If no, why not?
Thanks very much
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2017-07-19 08:55 AM
Link copied. Please paste this link to share this article on your social media post.
Thanks DICEA
Posted: 2017-07-19 09:01 AM
Link copied. Please paste this link to share this article on your social media post.
Hi DICEA,
But, case LINK 150_A include 5 PM5350 ( Connect modbus RS485)
LINK 150_B include 5 PM5350 (Conncect Modbus RS485)
So, also with a connect above, LINK 150_A will transaction total 10 PM 5350 to PC?
Thanks DICEA
Link copied. Please paste this link to share this article on your social media post.
Your ModbusTCPIP Client software will be able to see the meters grouped under 2 x IP addresses.
You will not see 10 meters under 1 IP, that of Link 150_B (192.168.1.20). You will see only those 5 meters that are connected over RS485 to this meter.
You will not see 10 meters under 1 IP, that of Link 150_A (192.168.1.30). You will see only those 5 meters that are connected over RS485 to this meter.
1 x Link 150 = 1 x ModbusTCPIP Server = 5 x PM5350
Ethernet Ports on Link 150_B (192.168.1.20) will act as a simple Ethernet switch and will pass over the ModbusTCPIP frames to your PC (ModbusTCPIP Client).
Regards,
Adrian
Posted: 2017-07-19 10:02 AM
Link copied. Please paste this link to share this article on your social media post.
HI DICEA,
It mean i can use 5 PM 5350 for once LINK 150.
Image below. Can I read value of PM5350 ID: 4. on PME software?
Thanks very much
Link copied. Please paste this link to share this article on your social media post.
Yes. That should work.
In fact, because you will access the ID=1 and ID=2 under different IP than ID=3 and ID=4, you can even have the same IDs: ID=1 and ID=2 for the meters under the second IP, as for the meters under the first IP.
Posted: 2017-07-19 10:17 AM
Link copied. Please paste this link to share this article on your social media post.
Thanks very much DICEA
Link copied. Please paste this link to share this article on your social media post.
Link 150 (EGX150) dosen't support Daisy chanin on the Ethernet ports.this will not work
Link copied. Please paste this link to share this article on your social media post.
The architecture in the picture should work right
Link copied. Please paste this link to share this article on your social media post.
Hi Mahmoud,
If you have troubles with such configuration, please raise a support ticket.
As far as I know (and tested in my lab) this configuration works without issues.
Ta Cong have you implemented that configuration? Was it working for you?
Thank you for feedback.
Regards,
Adrian
Link copied. Please paste this link to share this article on your social media post.
Hi,
I'll ask the team to teste it by next week and let you know
Regards
Link copied. Please paste this link to share this article on your social media post.
Hi Mahmoud
It works fine, I did the test
Regards
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.