Communication between two Com'X 510 + zigbee
Hello !
I connected two com'x 510 together on the same network.
The first has several equipment connected to it.
The second has zigbee counters connected to it
I added on the first com'x the second com'x as gateway.
I would like to know, if it is possible to read the data of the zigbee counters from the first com'x.
Thanks
François
Reply 1

Anonymous user
Not applicable
Posted: 2017-06-01 12:06 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
2017-06-01
12:06 PM
Hi,
Yes it is possible to read the values over modbus, the register map is provided in the ComX510 user manual.
Best Regards,
Colton