ComX510 and BMS reading meters

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • ComX510 and BMS reading meters
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
99
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
44
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Mark_Raftery
Ensign Mark_Raftery Ensign
Ensign

Posted: ‎2018-05-24 06:12 AM

0 Likes
2
647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-05-24 06:12 AM

ComX510 and BMS reading meters

Hi,

I have been looking at some threads here and would like to see if anyone has some ideas.

A normal install for us is, PM5111 or iEM3255 on a modbus network connected to a ComX510 with GRPS sending data to EDV or RA PAM.

We have a couple of enquiries where a BMS wants to see meter data as well.

I do not want the meters to be connected to the BMS and then the BMS send data to us. What I want is to allow the BMS to connect to the ComX and get the meter data separately or from a modbus table in the ComX.

I have seen a thread talking about using an EGX150 or Link150 and setting up the meters as IP addresses. This sounds very simple if two masters can conect tot this device and separate gather data. Is this the best solution or could the BMS connect to the Ethernet port on the ComX and read meter data that way.

Has anyone had any experience doing this, before I buy a Link150 and try? Or thoughts on another souloution or thread on here that I may have missed

Regards from Mark

Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Adria_Casas
Lieutenant JG Adria_Casas Lieutenant JG
Lieutenant JG

Posted: ‎2018-07-04 07:33 AM

0 Likes
0
621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-04 07:33 AM

Hi Mark,

the Com'X can do both at the same time: act as a datalogger to publish data to RA/PAM (or other cloud based system) and as a Modbus RTU/TCP gateway, so you can read "downstream" devices from another system (BMS in your case).

By default, this Modbus Gateway functionality is disabled, so In order to do achieve that, you might need to configure some settings under the Communications, Security AND Firewall settings pages.

After that, you should be able to read any Modbus RTU device connected to the COM'X as you would do with any other Modbus Gateway (EGX100, Link150, etc), and even the digital and analog outputs using the modbus tables in the Com'x manual.

A Modbus TCP/IP gateway should be able to handle several masters, and if there's any limitation to the number of connections it would probably be due to the Serial bus bandwidth

Hope this helps

Reply
greg_expoenergy
Lt. Commander greg_expoenergy
Lt. Commander

Posted: ‎2018-07-04 12:36 PM

0 Likes
0
621
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-07-04 12:36 PM

Hi Mark,

To add to what has been noted above by Adria.

As I understand matters you normally use the COM'X to connect to these meters and send data via GPRS.

One presumes that you do this via Modbus serial using the RS 485 port on of the COM'X.

If this is so then all you have to do is to connect the BMS to the COM'X Ethernet port and access the meters via the IP and slave address.

Thus the meters will be accesses by EDV or RA PAM via Ethernet via 3G and by the BMS via the COM'X Ethernet port and this should work fine. No need for any EGX150.

CURRENT

EDV / R PAM  -----   3G ------- COM'X ---------- RS 485 ------------ Meter Slave 1 ------- Meter Slave n

PROPOSED

EDV / R PAM --- 3G --------------------

                                                         |  --- COM'X ---- RS 485 --------------- Meter Slave 1 ------- Meter Slave n

BMS ------------> Ethernet Port 1 -----

This is shown below.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of