ComX200 - stuck in Boot screen.

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • ComX200 - stuck in Boot screen.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
mcolston
Lt. Commander mcolston
Lt. Commander

Posted: ‎2018-04-10 09:07 AM

0 Likes
5
1106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-04-10 09:07 AM

ComX200 - stuck in Boot screen.


I have commissioned a ComX 200 onto the network with some meters and have been waiting for the network point to be added to the Vlan.

This has now been done and this morning I noticed the ethernet port 1 was not allowing Modbus data onto the port - so i changed the setting and after a short while rebooted.

It is now hanging with the "This box is rebooting" message on the web browser.

It has remained in this state for about 9hours (I was working remotely via a vpn connection onto the site)

Is it a case of returning to site to fix the issue, or can a remote reset somehow be performed - which is the preferred option as it is a 230mile round trip from the office

Mark Colston
adi Intelligent Buildings Ltd
Tags (1)
  • Tags:
  • comx200
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 5
Anonymous user
Not applicable

Posted: ‎2018-04-11 06:14 AM

0 Likes
1
1075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-04-11 06:14 AM

Hi Mark,

Welcome to the frustrating world of Com’X....

Can’t you get a FM bod on site to power cycle the Com’X? That usually solves it. It’s a day trip otherwise.

Kind regards.

Reply
mcolston
Lt. Commander mcolston
Lt. Commander

Posted: ‎2018-04-17 02:17 AM

0 Likes
0
1075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-04-17 02:17 AM

Sorry for the long delay in replying.

That is one option - but I have an easier one! I'm going back to the same site this week to change some IP addresses on some other ComX's which the client decided to change after it was commissioned

Mark Colston
adi Intelligent Buildings Ltd
Reply
Anonymous user
Not applicable

Posted: ‎2018-04-18 08:04 AM

0 Likes
2
1075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-04-18 08:04 AM

Hi Mark,

Our support should be able to take a look remotely if you can get them IP access. Can you open a support ticket?

Best,
Colton

Reply
mcolston
Lt. Commander mcolston
Lt. Commander

Posted: ‎2018-04-26 04:19 PM

0 Likes
1
1075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-04-26 04:19 PM

Thanks I sorted it on Monday as I had to go back to sort some heat meters on the same site.

Interestingly I also found that the ComX was powered via POE - so had to remove both power sources - I guess this isn't an issue?

Mark Colston
adi Intelligent Buildings Ltd
Reply
Anonymous user
Not applicable

Posted: ‎2018-04-27 10:36 AM

0 Likes
0
1075
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-04-27 10:36 AM

Hi Mark,

Glad to hear its working for you now. The PoE can be used as a backup power source, so the ComX being able to swith between power sources is a feature!

Best

Colton

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore