ComX GPRS

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • ComX GPRS
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
sesa237527
sesa237527 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-09-21 10:51 PM

0 Likes
10
3887
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-09-21 10:51 PM

ComX GPRS

I am looking at the technical documentation on the GPRS unit for a ComX, is it 2G or 3G?

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
sesa22585
sesa22585 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-09-22 07:11 AM

1 Like
6
3730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-09-22 07:11 AM

The GPRS accessory in the catalog is 2G.  With the latest firmware (V3.0) - you can also use a 3G dongle.  Here are the part numbers for three 3G references we have tested and recommend with the Com'X. 

These are the models supported on the Com'X (in order of recommendation):

  • MultiTech MTC-H5-B03-KIT (http://www.multitech.com/datasheets/86002164.pdf)
  • Huawei MS2131i-8
  • MultiTech MTD-H5 (http://www.multitech.com/models/92507090LF)

See Answer In Context

Reply
Replies 10
sesa22585
sesa22585 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-09-22 07:11 AM

1 Like
6
3731
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-09-22 07:11 AM

The GPRS accessory in the catalog is 2G.  With the latest firmware (V3.0) - you can also use a 3G dongle.  Here are the part numbers for three 3G references we have tested and recommend with the Com'X. 

These are the models supported on the Com'X (in order of recommendation):

  • MultiTech MTC-H5-B03-KIT (http://www.multitech.com/datasheets/86002164.pdf)
  • Huawei MS2131i-8
  • MultiTech MTD-H5 (http://www.multitech.com/models/92507090LF)
Reply
Coppo
Lt. Commander Coppo Lt. Commander
Lt. Commander

Posted: ‎2016-09-26 07:10 PM

0 Likes
2
3730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-09-26 07:10 PM

Is it correct that when selecting the GPRS "USB" connect method.... you lose the seperate ethernet connectivity on the dual RJ45's on ComX 510?  

Reply
sesa237527
sesa237527 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2016-09-26 08:33 PM

0 Likes
1
3730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-09-26 08:33 PM

Hi Brett.  I can't help with this question, I recommend you reach out to the wider subject space for comments.

Reply
Coppo
Lt. Commander Coppo Lt. Commander
Lt. Commander

Posted: ‎2016-09-26 09:19 PM

0 Likes
0
3730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2016-09-26 09:19 PM

Sorry, I was actually adrressing my question to bobbie meredith, but clicked on the wrong link.

Reply
Coppo
Lt. Commander Coppo Lt. Commander
Lt. Commander

Posted: ‎2017-01-05 02:48 PM . Last Modified: ‎2022-10-18 10:28 PM

0 Likes
0
3730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-01-05 02:48 PM

referring to "tested", does that mean  the 3 products listed are directly supported simply by plugging them into a USB port on the ComX unit and powering up the ComX?

same as how the EBXA-GPRS is currently detected.... ie:   no firmware update required?

based upon the physical format of these new alternatives and limitations, ie none look to fit under the existing comx cover, and the Huawei unit does not look available in AU, we will continue recommending ethernet connection instead as per

https://community.se.com/message/98765#98765

Reply
Coppo
Lt. Commander Coppo Lt. Commander
Lt. Commander

Posted: ‎2017-01-30 09:18 PM

0 Likes
4
3730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-01-30 09:18 PM

Bobbie,
The previous serial modem EBXA-GPRS was data publish "dial-out only" from ComX unit.

These 3 new units you advise are tested and recommended are all "serial modems" I expect.
So they will still have the same data publish "dial-out only" functionality I would assume. 

My understanding is that unless the ComX is connected to ethernet via a VPN supporting USB modem/router/switch,
I will not be able to dial into it from external TELCO connection.

Reply
Anonymous user
Not applicable

Posted: ‎2017-02-01 11:33 AM

0 Likes
3
3730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-02-01 11:33 AM

Hi Brett,

Can you clarify what you mean by "dial out only" functionality? What is it you would like to do with the ComX over 3G?

Best,

Colton Peltier

Reply
Coppo
Lt. Commander Coppo Lt. Commander
Lt. Commander

Posted: ‎2017-02-01 02:41 PM

1 Like
2
3729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-02-01 02:41 PM

Dial-out.... the device (comX) can send data out to another machine/service.

I have read and also been told by our local trainers that ComX via the serial modem only supports 1 way comms...

so it can data publish "dial-out only", but cannot be dialed into from the existing schneider 2G modem EBXA-GPRS.

For you to remote access into the ComX you would need to have it connected via ethernet and typically a modem/router/switch allowing VPN connection, so the ComX thinks you are on the local network.

Ethernet connection is the recommended connection we have documented here in AU, using suitable local products already approved for use on our local TELCO.

For you to remote access any of the data info on a ComX that is using a EBXA-GPRS, you can't directly.  The info would have to be sourced from a cloud service that the ComX is publishing data into, such as "Facilities Insights" or similar.   

Reply
Anonymous user
Not applicable

Posted: ‎2017-02-02 05:16 AM

0 Likes
1
3730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-02-02 05:16 AM

Hi Brett,

Thank you for the clarification. Depending on your cellular provider and ComX model, it may be possible for you to "dial-in" to the ComX. However, it may be very slow depending on the connection. What ComX model are you using?

Best,

Colton

Reply
Coppo
Lt. Commander Coppo Lt. Commander
Lt. Commander

Posted: ‎2017-02-02 02:32 PM

1 Like
0
3729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-02-02 02:32 PM

ComX 510.

FYI.

The manufacturer has responded to local team and advised the MTC-H5-B03 is designed for data-publish out from ComX unit only.

 

MultiTech Manufacturer states that "if we require 2 way communications" we should look at one of their more expensive products that is a ethernet router/modem (MTR-H5/H6) , as the MTC-H5-B03  product is only a simple serial modem and does not natively support VPN/DDNS support etc for remote connection into ComX.


They mention about being able to support auto IP connection, but that it would require someone to write a program into the MTC-H5-B03 using python so it can auto configure or set itself up as a server.

In my personal opinion, this all sounds like a potential point of failure in a 3rd party product ' that Schneider would end up having to warranty".

Much better to go with the "ethernet connect" options that I documented previously that natively support VPN direct from  their own manufacturers and would not need to be exhaustively tested to ensure the functionality of the ComX is intact.      

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore